Continuous Thermal Monitoring in Low Voltage equipments?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Continuous Thermal Monitoring in Low Voltage equipments?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
Okken
product field
Schneider Electric
EcoStruxure™ Power Monitoring Expert
product field
Schneider Electric
Canalis Busbar Trunking System
field url
Schneider Electric
BlokSet
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2020-09-03 09:51 AM . Last Modified: ‎2020-11-25 04:11 AM

2 Likes
12
6788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-03 09:51 AM . Last Modified: ‎2020-11-25 04:11 AM

Continuous Thermal Monitoring in Low Voltage equipments?

Dear Community,

 

I've seen many information regarding Continuous Thermal Monitoring (using TH110 sensors + apps) for Medium Voltage Switchgears but I wonder if it exists the same devices to monitor temperature in a LV equipment and then reduce infrared inspections and protect against overheating.

If yes, where could I find more insights.

 

Thanks for your answer.

Labels
  • Labels:
  • Power Availability
  • Products
  • Safety - Electrical Fire Prevention
  • Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-09-08 03:30 AM

3 Likes
1
6766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 03:30 AM

Hello, 

 

We have already installed the sensors in several cases on copper bars, near critical components.

The question if this could change the infrared inspections: 

Yes. The advantage is that you have a continious measurement in stead of a one moment picture. 

The question is better if you assurance will agree with this changed control procedure. 

 

Please check the link below for a practical case.

 

https://www.linkedin.com/posts/stijncuppens_teamwork-oneabrstepabraheadabrinabrservice-activity-6696...

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-26 11:06 AM

In response to Anonymous user
3 Likes
7
6619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-26 11:06 AM

Hello Charlie, 

 

For busways you can use the CL110. 

Check 

https://www.se.com/ww/en/product/FSRACOBUSWAYCL110/busway-jonction-box-upgrade-with-2-cl110/

Kind regards.

Stijn

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Fabien_Mastrot
Fabien_Mastrot Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-09-07 08:51 AM

0 Likes
0
6772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-07 08:51 AM

Hello,

yes the Thermal Sensor TH110 can be also installed in Blokset and Okken LV equipment. 

You can publish the date on the Software Power Monitoring Expert .

How can we help you more ?

Rgds

Fabien

Fabien Mastrot
EcoXpert global badge owner
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-08 03:30 AM

3 Likes
1
6767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 03:30 AM

Hello, 

 

We have already installed the sensors in several cases on copper bars, near critical components.

The question if this could change the infrared inspections: 

Yes. The advantage is that you have a continious measurement in stead of a one moment picture. 

The question is better if you assurance will agree with this changed control procedure. 

 

Please check the link below for a practical case.

 

https://www.linkedin.com/posts/stijncuppens_teamwork-oneabrstepabraheadabrinabrservice-activity-6696...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2020-09-08 07:54 AM

In response to Anonymous user
0 Likes
0
6761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 07:54 AM

Thanks a lot @Fabien_Mastrot and @Anonymous user for your insights.

 

Regards.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-24 02:06 AM

0 Likes
8
6650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 02:06 AM

Hi,

Few times, I have done installation of high power busway, from Schneider and other manufacturer. One of the key points where a problem linked to overheat can occur is in the joints. I was thinking that maybe this sensor could be also of use in this cases. Are you planning to include it as an option in your busway offer? Could it be used in busways from other manufacturers? Thanks in advance

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-26 11:06 AM

In response to Anonymous user
3 Likes
7
6620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-26 11:06 AM

Hello Charlie, 

 

For busways you can use the CL110. 

Check 

https://www.se.com/ww/en/product/FSRACOBUSWAYCL110/busway-jonction-box-upgrade-with-2-cl110/

Kind regards.

Stijn

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2020-12-02 07:33 AM

In response to Anonymous user
3 Likes
5
6233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-02 07:33 AM

Dear community,

 

Regarding thermal monitoring solutions (to reduce infrared thermal inspections), I’ve been talked about another technology that uses small infrared permanent sensors positioned inside the switchgear in front of each busbar.

 

Does someone already used this technology for thermal monitoring needs?

What is your experience?

What do you think of this solution?

Is it easy to install?

 

Thanks for sharing your thoughts

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gingko_Elec
Lieutenant JG Gingko_Elec
Lieutenant JG

Posted: ‎2020-12-09 06:59 AM

In response to L_Valentin
1 Like
4
6153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-09 06:59 AM

Hello,

How do you monitor heating 24/7 using this technology?

I mean: is there any native supervision software or is it compatible with others (such as the Schneider Electric’s one as example)?

Is it wireless connected to the management system?

What would be the advantages?

Thanks for sharing

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-12-09 12:54 PM . Last Modified: ‎2020-12-09 12:57 PM

In response to Gingko_Elec
1 Like
3
6147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-09 12:54 PM . Last Modified: ‎2020-12-09 12:57 PM

Hello, 

 

 

Correct. You can get 24/7 data out of the thermal sensors. They connect with wireless zigby to a concentrator and can than be connected to a network. (Ecostruxure or other)

IMG-20200802-WA0018.jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2020-12-09 11:15 PM

In response to Anonymous user
0 Likes
2
6142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-09 11:15 PM

Hello @Anonymous user 

 

Thanks for sharing your experience.

 

However, it seems that you are talking about Schneider Electric (I can see their sensors into your picture 😁 ) and I guess @Gingko_Elec was wondering about the technology (infrared local sensors) I was mentionning previously.

 

Do you know about it?

Any thought?

 

Thks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-12-09 11:22 PM

In response to L_Valentin
1 Like
1
6140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-09 11:22 PM

Hello, 

 

Local infrared sensors I don't have any experience with. 

We have already placed heat stickers, but this still needs visual inspection to get info out of it, and it doesn't create an alarm to warn you.

 

IMG_20190326_133012.jpg 

 

Greetings 

Stijn

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

L_Valentin
Lt. Commander L_Valentin
Lt. Commander

Posted: ‎2020-12-14 11:51 PM

In response to Anonymous user
0 Likes
0
6039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-14 11:51 PM

Thanks for sharing your experience @Anonymous user .

 

Indeed, it seems that the "sticker" solution is not as relevant.

 

I am looking for a solution that reduces infrared inspection while alarming when there is an issue.

 

The infrared "local" sensors technology seemed easy to implement but too many questions... too few answers.... 😁

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gig_DSA
Crewman Gig_DSA Crewman
Crewman

Posted: ‎2023-02-20 12:17 PM

In response to Anonymous user
0 Likes
0
3669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-20 12:17 PM

Hi, Can CL110 attach to the Canalis busway with the magnets? & the second thing, do we actually have the analytics (with compensation factors since the sensor is outside not inside the copper/aluminum) to analyze the data correctly in EAA?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore