Conductor sizing between main distribution block and submain busbar within an enclosure

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Conductor sizing between main distribution block and submain busbar within an enclosure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-10-28 09:52 AM . Last Modified: ‎2021-10-28 10:06 AM

0 Likes
4
3905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-28 09:52 AM . Last Modified: ‎2021-10-28 10:06 AM

Conductor sizing between main distribution block and submain busbar within an enclosure

Greeting, In Linergy catalogue (Reference LVYED213001EN) on pages 6 and 7 there is a depiction of submain busbars of several rows being fed from main distribution block. How are cross section and insulation material properties of these conductors being determined given that they are not overload protected and possibly not short-circuit protected due to cross section being decreased?

Labels
  • Labels:
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-08 06:47 AM . Last Modified: ‎2021-11-08 06:50 AM

3 Likes
0
3820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-08 06:47 AM . Last Modified: ‎2021-11-08 06:50 AM

Hello @Anonymous user 

 

Regarding  question : How are cross section and insulation material properties of these conductors being determined given that they are not overload protected and possibly not short-circuit protected due to cross section being decreased?

 

Regarding cross-section about rating, the cables are sizing at the same rating of the distribution block. They are tested according that performance with the IEC61439-2 as built-in components.

Regarding cross section about short-circuit, the cable are sizing taking to account about the coordination performance between upstream and down stream performance. The worst case performances has been tested.

 

The standard IEC61439-1/2 precise :

8.6.1 Main circuits

The busbars (bare or insulated, see 3.1.5) shall be arranged in such a manner that an internal

short-circuit is not to be expected. They shall be rated at least in accordance with the requirements concerning the short-circuit withstand strength (see 9.3) and designed to

withstand at least the short-circuit stresses limited by the protective device(s) on the supply side of the busbars.

 

This rule is important because if not, we should size for example the cross section of connection to distribution block or MCCB breakers connected to the distribution busbar with the same cross section of the main busbar dimensioned to ICC or ICW.

 

Best regards,

 

PascalL.

pascal.lepretre@se.com

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-01 01:23 AM . Last Modified: ‎2021-11-01 01:25 AM

1 Like
2
3876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-01 01:23 AM . Last Modified: ‎2021-11-01 01:25 AM

Hello @Anonymous user ,

I do not know how the insulation thickness etc. is tested and determined as I am not a manufacturer of these distribution blocks.
There are probably standards and regulations for this. Perhaps Schneider Electric could give a full answer.

However just like your head switch in your panel, is just a ''switch''. There is no protection from the standard switch.
The standard switch will burnout by exceeding its capable Amperage, this will be the same for your distribution block.
Thats why most of the panels are protected by fuses at the transformer side or main switchboard. (Or if protection is not at the transformer, main switch of the panel = fuse / breaker).

Your distribution (blocks) do not need to have protecting capabilities as the protection is at your transformer (feeding side) or your breakers (user side). It only has one use, that is distributing currents to your breakers.

 

 

 


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-01 12:58 PM

In response to RHH
1 Like
1
3868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-01 12:58 PM

Hello, @RHH. My question wasn't about main distribution block which is downstream of the main switch/main circuit breaker as sizing it is pretty straightforward because as you've mentioned it most likely is being overload and short-circuit protected by either main circuit breaker or some other device upstream. My question was about how do you size busbars and their conductors immedietly downstream of main distribution block (for example comb busbars connecting multiple MCBs and conductor suppying it) which aren't short-circuit and overload protected.

As for conductors and their insulation material properties which aren't short circuit protected I think I found the answer. Looks like according to IEC 61439-1 such conductors with 70deg C PVC insulation have to be routed away from any combustible materials. 90deg C PVC ones don't have any particular requirements.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-02 02:16 AM . Last Modified: ‎2021-11-02 02:22 AM

In response to Anonymous user
1 Like
0
3862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-02 02:16 AM . Last Modified: ‎2021-11-02 02:22 AM

Hey @Anonymous user ,

 

Correct, what I was trying to say is there are no regulations concerning the busbars in the meaning of protection.

Cause they don't have to. They are not there to protect anything and the chance of being the concern or cause of an defect is slim to very low, as panel builders follow IEC while building and wiring them. However the bigger copper/aluminum (250A+) rail bars have a max. kA value that can be hightened with more supports closer to eachother.

As in the standard regulations state; you need to wire the mcb's with the correct copper/cable thickness for the amperage.
As far as I know of, most of the bars I know are fit for 80A. (industrial) But this is not a certainty with lots of different bars out there.

I didn't know of and about the certain thickness and insulation requirements, thanks for the involvement and insight in that matter. As I previously mentioned someone would know about these specification exactly from the manufacterer, like Schneider Electric.

We as panel builder standardized 90 degrees in wiring etc. a while ago, might be the reason we have not been looking into the specifications that deeply anymore. Again thanks for the heads up!


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

PascalL
PascalL Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-08 06:47 AM . Last Modified: ‎2021-11-08 06:50 AM

3 Likes
0
3821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-08 06:47 AM . Last Modified: ‎2021-11-08 06:50 AM

Hello @Anonymous user 

 

Regarding  question : How are cross section and insulation material properties of these conductors being determined given that they are not overload protected and possibly not short-circuit protected due to cross section being decreased?

 

Regarding cross-section about rating, the cables are sizing at the same rating of the distribution block. They are tested according that performance with the IEC61439-2 as built-in components.

Regarding cross section about short-circuit, the cable are sizing taking to account about the coordination performance between upstream and down stream performance. The worst case performances has been tested.

 

The standard IEC61439-1/2 precise :

8.6.1 Main circuits

The busbars (bare or insulated, see 3.1.5) shall be arranged in such a manner that an internal

short-circuit is not to be expected. They shall be rated at least in accordance with the requirements concerning the short-circuit withstand strength (see 9.3) and designed to

withstand at least the short-circuit stresses limited by the protective device(s) on the supply side of the busbars.

 

This rule is important because if not, we should size for example the cross section of connection to distribution block or MCCB breakers connected to the distribution busbar with the same cross section of the main busbar dimensioned to ICC or ICW.

 

Best regards,

 

PascalL.

pascal.lepretre@se.com

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore