Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-02 02:17 AM . Last Modified: 2022-05-02 03:00 AM
hello there
Is it possible to use the existing 3-phase 4-wire circuit breaker Micrologic7 as a single-phase 3-wire type?
Best Regard.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-04 07:23 AM
Hello @Hyeontae-Song ,
Thanks for raising the topic, this is not well documented in our catalog.
This may be possible with Micrologic 7, but only under specific conditions. Therefore I cannot answer here, I suggest you to contact Schneider Customer Care Center and mention my name.
Christian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-02 03:05 AM . Last Modified: 2022-05-02 03:06 AM
Hello @Hyeontae-Song,
I saw that you've joined a wiring diagram related to your question into the "cover photo" section.
However, we cannot really see it.
Would it be possible to add it directly into the "Body" section of the post by replying below?
(see button to use below 👇)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-02 08:31 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-02 08:31 AM
Hello,
I don t think so . I let some experts confirm but from a Technology stand point I can not see how it can work .
Guys any inputs on it ?
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-03 12:23 AM . Last Modified: 2022-05-03 12:54 AM
Hello @Hyeontae-Song ,
Can you please confirm your network voltage ? 220V Phase to phase & 110V Phase to neutral ?
Thanks.
Christian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-03 03:44 AM
Hello.
Thank you for your interest.
Attached is a picture related to the wiring method.
Best Regard.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-04 07:23 AM
Hello @Hyeontae-Song ,
Thanks for raising the topic, this is not well documented in our catalog.
This may be possible with Micrologic 7, but only under specific conditions. Therefore I cannot answer here, I suggest you to contact Schneider Customer Care Center and mention my name.
Christian