Clarification on DOs to be used for Arc-Flash protection function with Easergy P5x30

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Clarification on DOs to be used for Arc-Flash protection function with Easergy P5x30
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
GiuliaMorandi
GiuliaMorandi Cadet
Cadet

Posted: ‎2021-04-09 06:16 AM . Last Modified: ‎2021-05-05 11:25 PM

0 Likes
1
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-09 06:16 AM . Last Modified: ‎2021-05-05 11:25 PM

Clarification on DOs to be used for Arc-Flash protection function with Easergy P5x30

Hi there,

 

I'm writing to call out P5 users/experts part of the community for a clarification about DOs to be associated to Arc stages in P5x30 Arc-Flash protection.

 

Useful information on this topic from the User's manual are:

Characteristics of the Arc-Flash protection function (as per table 68, screenshot attached here)
  -> according to this table high speed operation can be obtained with high speed,high break contacts

 

Tab68_1.PNG

 

Tab68_2.PNG

 

Technical characteristics of relay DOs (as per table 4, meaningful parts again attached here)
  -> according to this table there's no high speed DO in P5x30 Arc-Flash module

 

Tab4_1.PNGTab4_2.PNGTab4_3.PNG


Given the above info:

- Should Arc stages be associated to high speed,high-break control output relays only?
- What operating time can be obtained by associating Arc stages to normal non-high speed,high-break control output relays instead? Still in the range compatible with arc mitigation?

 

 

Thanks in advance for support,

 

Labels
  • Labels:
  • Connectivity
  • Products
  • Safety - People Safety
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2021-04-13 06:51 AM

1 Like
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-13 06:51 AM

Using the high speed, high-break relay output provides best operation of arc-flash protection, hence it is recommended to use it.

Worth to notice that this output is designed for CB trip command application, so circuit wear is no issue.

 

Using any other command rated P5 relay output introduces a typical operation delay of 6 to 7 ms (due to the mechanical inertia of the output contact). 

Whether arc flash protection operation then is still acceptable depends on local requirements/ user expectations/ ...

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2021-04-13 06:51 AM

1 Like
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-13 06:51 AM

Using the high speed, high-break relay output provides best operation of arc-flash protection, hence it is recommended to use it.

Worth to notice that this output is designed for CB trip command application, so circuit wear is no issue.

 

Using any other command rated P5 relay output introduces a typical operation delay of 6 to 7 ms (due to the mechanical inertia of the output contact). 

Whether arc flash protection operation then is still acceptable depends on local requirements/ user expectations/ ...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore