Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Anonymous user
Not applicable

Posted: ‎2019-06-19 08:57 AM . Last Modified: ‎2020-11-20 03:53 AM

0 Likes
1
3590
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-06-19 08:57 AM . Last Modified: ‎2020-11-20 03:53 AM

Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength

Could you please indicate in what cases circuits of Assemblies are exempted from the verification of the short-circuit withstand strength according to IEC 61439-1 and how we can apply this rule with limitor circuit-breaker ?

Labels
  • Labels:
  • Connectivity
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2019-07-02 05:27 AM . Last Modified: ‎2021-06-21 05:21 AM

1 Like
0
3548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-07-02 05:27 AM . Last Modified: ‎2021-06-21 05:21 AM

Elina

 

The Clause 10.11.2 of IEC 61439-1 exempt from doing a short circuit test in two cases:

10.11.2 Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength

A verification of the short-circuit withstand strength is not required for the following:

1) ASSEMBLIES having a rated short-time withstand current (see 5.3.5) or rated conditional short-circuit current (see 5.3.6) not exceeding 10 kA r.m.s.

2) ASSEMBLIES protected by current-limiting devices having a cut-off current not exceeding 17 kA at the maximum allowable prospective short-circuit current at the terminals of the incoming circuit of the ASSEMBLY.

 

According to the second bullet, it’s possible to use the limitation characteristics of compact NSX & NSXm to avoid a short-circuit test for prospective short-circuit current that will be limited below 17kApeak

 

NSX NSXm Limitation curves.PNG

 

So the following values can be keep as a rule:

 

 

Incomer circuit-breaker

Icu (kA)

@415V

Maximum presumed short-circuit current in kArms where IEC 61439 sort-circuit withstand test is not required

(Clause 10.11.2 -2) with specified incomer : 415Vac 50Hz

Compact NSXm 160 E

16kA

16kA

Compact NSXm 160 B

25kA

25kA

Compact NSXm 160 F

36kA

36kA

Compact NSXm 160 N

50kA

50kA

Compact NSX100-160 B

25kA

25kA

Compact NSX100-160 F

36kA

36kA

Compact NSX250 B

25kA

25kA

Compact NSX250 F

36kA

30kA

Compact NSX400 F

36kA

15kA

Compact NSX630 F

36kA

12kA

 

 

Mathieu GUILLOT

LV Power circuit-breakers 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2019-07-02 05:27 AM . Last Modified: ‎2021-06-21 05:21 AM

1 Like
0
3549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-07-02 05:27 AM . Last Modified: ‎2021-06-21 05:21 AM

Elina

 

The Clause 10.11.2 of IEC 61439-1 exempt from doing a short circuit test in two cases:

10.11.2 Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength

A verification of the short-circuit withstand strength is not required for the following:

1) ASSEMBLIES having a rated short-time withstand current (see 5.3.5) or rated conditional short-circuit current (see 5.3.6) not exceeding 10 kA r.m.s.

2) ASSEMBLIES protected by current-limiting devices having a cut-off current not exceeding 17 kA at the maximum allowable prospective short-circuit current at the terminals of the incoming circuit of the ASSEMBLY.

 

According to the second bullet, it’s possible to use the limitation characteristics of compact NSX & NSXm to avoid a short-circuit test for prospective short-circuit current that will be limited below 17kApeak

 

NSX NSXm Limitation curves.PNG

 

So the following values can be keep as a rule:

 

 

Incomer circuit-breaker

Icu (kA)

@415V

Maximum presumed short-circuit current in kArms where IEC 61439 sort-circuit withstand test is not required

(Clause 10.11.2 -2) with specified incomer : 415Vac 50Hz

Compact NSXm 160 E

16kA

16kA

Compact NSXm 160 B

25kA

25kA

Compact NSXm 160 F

36kA

36kA

Compact NSXm 160 N

50kA

50kA

Compact NSX100-160 B

25kA

25kA

Compact NSX100-160 F

36kA

36kA

Compact NSX250 B

25kA

25kA

Compact NSX250 F

36kA

30kA

Compact NSX400 F

36kA

15kA

Compact NSX630 F

36kA

12kA

 

 

Mathieu GUILLOT

LV Power circuit-breakers 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of