Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Posted: 2019-06-19 08:57 AM . Last Modified: 2020-11-20 03:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-06-19 08:57 AM . Last Modified: 2020-11-20 03:53 AM
Could you please indicate in what cases circuits of Assemblies are exempted from the verification of the short-circuit withstand strength according to IEC 61439-1 and how we can apply this rule with limitor circuit-breaker ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-07-02 05:27 AM . Last Modified: 2021-06-21 05:21 AM
Elina
The Clause 10.11.2 of IEC 61439-1 exempt from doing a short circuit test in two cases:
10.11.2 Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength
A verification of the short-circuit withstand strength is not required for the following:
1) ASSEMBLIES having a rated short-time withstand current (see 5.3.5) or rated conditional short-circuit current (see 5.3.6) not exceeding 10 kA r.m.s.
2) ASSEMBLIES protected by current-limiting devices having a cut-off current not exceeding 17 kA at the maximum allowable prospective short-circuit current at the terminals of the incoming circuit of the ASSEMBLY.
According to the second bullet, it’s possible to use the limitation characteristics of compact NSX & NSXm to avoid a short-circuit test for prospective short-circuit current that will be limited below 17kApeak
So the following values can be keep as a rule:
Incomer circuit-breaker |
Icu (kA) @415V |
Maximum presumed short-circuit current in kArms where IEC 61439 sort-circuit withstand test is not required (Clause 10.11.2 -2) with specified incomer : 415Vac 50Hz |
Compact NSXm 160 E |
16kA |
16kA |
Compact NSXm 160 B |
25kA |
25kA |
Compact NSXm 160 F |
36kA |
36kA |
Compact NSXm 160 N |
50kA |
50kA |
Compact NSX100-160 B |
25kA |
25kA |
Compact NSX100-160 F |
36kA |
36kA |
Compact NSX250 B |
25kA |
25kA |
Compact NSX250 F |
36kA |
30kA |
Compact NSX400 F |
36kA |
15kA |
Compact NSX630 F |
36kA |
12kA |
Mathieu GUILLOT
LV Power circuit-breakers
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-07-02 05:27 AM . Last Modified: 2021-06-21 05:21 AM
Elina
The Clause 10.11.2 of IEC 61439-1 exempt from doing a short circuit test in two cases:
10.11.2 Circuits of ASSEMBLIES which are exempted from the verification of the short-circuit withstand strength
A verification of the short-circuit withstand strength is not required for the following:
1) ASSEMBLIES having a rated short-time withstand current (see 5.3.5) or rated conditional short-circuit current (see 5.3.6) not exceeding 10 kA r.m.s.
2) ASSEMBLIES protected by current-limiting devices having a cut-off current not exceeding 17 kA at the maximum allowable prospective short-circuit current at the terminals of the incoming circuit of the ASSEMBLY.
According to the second bullet, it’s possible to use the limitation characteristics of compact NSX & NSXm to avoid a short-circuit test for prospective short-circuit current that will be limited below 17kApeak
So the following values can be keep as a rule:
Incomer circuit-breaker |
Icu (kA) @415V |
Maximum presumed short-circuit current in kArms where IEC 61439 sort-circuit withstand test is not required (Clause 10.11.2 -2) with specified incomer : 415Vac 50Hz |
Compact NSXm 160 E |
16kA |
16kA |
Compact NSXm 160 B |
25kA |
25kA |
Compact NSXm 160 F |
36kA |
36kA |
Compact NSXm 160 N |
50kA |
50kA |
Compact NSX100-160 B |
25kA |
25kA |
Compact NSX100-160 F |
36kA |
36kA |
Compact NSX250 B |
25kA |
25kA |
Compact NSX250 F |
36kA |
30kA |
Compact NSX400 F |
36kA |
15kA |
Compact NSX630 F |
36kA |
12kA |
Mathieu GUILLOT
LV Power circuit-breakers