Circuit breaker testing and questions

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Circuit breaker testing and questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
75
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
bujaam
bujaam
Cadet

Posted: ‎2024-09-14 04:38 AM

0 Likes
1
835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-14 04:38 AM

Circuit breaker testing and questions

Let me know if I have this right for the different tests performed on breakers. Is there an online resource for info on these tests?

Power factor - testing the Insulation of the bushing by applying a high voltage to the top and a lower voltage to the bottom of the same bushing of the same pole with the breaker open. I’m not sure what exactly we’re looking for here

Ductor - applying a high current across the contacts of a closed breaker and looking for a low resistance value. This seems pretty straight forward unless I’m missing something

Hi pt - applying a high voltage to the bushings of a breaker with one lead from the hi pt applying several kv to the breaker and another lead connected to ground(?). Used to check for leakage to ground through the insulating medium, I’m not sure how this works either.

Megger - same application as the hi-pt test?

Any help would be appreciated, I’m new and trying to learn about the different tests that are done

router login 192.168.l.l
Labels
  • Labels:
  • How to
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2024-09-18 06:31 AM

1 Like
0
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 06:31 AM

Hello @bujaam. Thank you for your post! 🙂 

 

This is the information I can add for the different tests:

  1. Power Factor Test:

    • The objective is to measure the power factor, which indicates the condition of the insulation. A lower power factor may suggest potential issues with the insulation.
  2. Ductor Test:

    • A low resistance value is generally expected, indicating good electrical continuity.
  3. Hi-Pot Test (High Potential Test):

    • It's used to check for leakage to ground through the insulating medium. If there is excessive leakage, it could indicate potential insulation issues.
  4. Megger Test:

    • The Megger test is used to measure the insulation resistance of the breaker. It involves applying a high voltage to the insulation and measuring the resistance.
    • It differs from the Hi-Pot test as it specifically focuses on insulation resistance.

As for online resources, I recommend referring to industry standards and resources for detailed information on these tests. Additionally, manufacturer documentation for specific breakers may provide detailed testing procedures.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2024-09-18 06:31 AM

1 Like
0
798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 06:31 AM

Hello @bujaam. Thank you for your post! 🙂 

 

This is the information I can add for the different tests:

  1. Power Factor Test:

    • The objective is to measure the power factor, which indicates the condition of the insulation. A lower power factor may suggest potential issues with the insulation.
  2. Ductor Test:

    • A low resistance value is generally expected, indicating good electrical continuity.
  3. Hi-Pot Test (High Potential Test):

    • It's used to check for leakage to ground through the insulating medium. If there is excessive leakage, it could indicate potential insulation issues.
  4. Megger Test:

    • The Megger test is used to measure the insulation resistance of the breaker. It involves applying a high voltage to the insulation and measuring the resistance.
    • It differs from the Hi-Pot test as it specifically focuses on insulation resistance.

As for online resources, I recommend referring to industry standards and resources for detailed information on these tests. Additionally, manufacturer documentation for specific breakers may provide detailed testing procedures.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore