Can the Acti 9 Residual current circuit breaker iID work under an operating voltage of 200-240 V AC 3 Phase ?
  • Power Distribution IEC
  • Can the Acti 9 Residual current circuit breaker iID work under an operating voltage of 200-240 V AC 3 Phase ?
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Kanon.w
Crewman Kanon.w
Crewman
Posted: ‎2025-10-30 07:04 PM
257
Hi Experts, can the Acti 9 Residual current circuit breaker Acti 9 iID work under an operating voltage of 200-240 V AC  3 Phase?
Referring to the iLD line of RCCBs.  Is it okay to do it and the protection is still working?
Acti 9 iID | Schneider Electric Singapore
Thank you!
  • Power Availability
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander
Posted: ‎2025-10-31 01:24 AM
Hello @Kanon.w, thank you for your post, we'll come back to you!
Gregoire_Brun
Commander
Posted: ‎2025-11-03 04:24 AM
Hello @Kanon.w
CCBs Acti9 iID are voltage independent products certified acc. to IEC/EN 61008-1 / -2-1 Stds however their test button function depends on the voltage.
So, test button of RCCBs Acti9 iID 4P Ue(L/L)=400-415Vac will not operate under Ue(L/L)=230-240Vac three-phases network, and there is specific product references of RCCBs Acti9 iID 4P e.g. : A9R08463 to use under Ue(L/L)=230-240Vac three-phases network
So we wouldn't recomend to use this product at this voltage.
Gregoire Brun
Breaker Product Expert
Kanon.w
Crewman Kanon.w
Crewman
Posted: ‎2025-11-03 05:12 PM
@Gregoire_Brun Thanks for the reply Gregorie,
So the test button doesn't work but the protection still works under that voltage range?
I saw 402642477, however there is only an option for 63A rated current. We needed one in 40A, 80A and 63A and 100mA sensitivity.
Thank you.