Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-19 12:21 AM
How to resolve that warning?:
"Cable termal constrait (i2t>k2s2) is exceded at 10 ms, please check if circuit breaker energy limitation curve validates k2s2<i2t for short circuit value, otherwise please increase cable cross section value oh [PH]"
I have tried increasing the cable section and it does not solve the problem.
I attach a file, thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-30 10:27 PM
hi @laumarher ,
thanks for the query!
this issue here is that Ecodial showed a “thermal constraint (I2t > k2S2) exceeded” warning for cables
This means that during a short-circuit, the energy passing through the cable (I2t) was higher than what the cable’s insulation and size could safely handle.
Reason:
The fault current at that point was around 12 kA, and the earlier cable size (1.5 – 10 sqmm) was too small to withstand that energy.
Workaround:
After increasing the cable size to 16 sqmm (Cu/PVC), the cable can now handle the short-circuit energy, and the warning is cleared.
so you might have tried to increase the CSA to 4 or 6sq.mm and that is not sufficient according to the constraints.
Hope that clarifies it for you!
Regards,
Darini H.D
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-30 10:27 PM
hi @laumarher ,
thanks for the query!
this issue here is that Ecodial showed a “thermal constraint (I2t > k2S2) exceeded” warning for cables
This means that during a short-circuit, the energy passing through the cable (I2t) was higher than what the cable’s insulation and size could safely handle.
Reason:
The fault current at that point was around 12 kA, and the earlier cable size (1.5 – 10 sqmm) was too small to withstand that energy.
Workaround:
After increasing the cable size to 16 sqmm (Cu/PVC), the cable can now handle the short-circuit energy, and the warning is cleared.
so you might have tried to increase the CSA to 4 or 6sq.mm and that is not sufficient according to the constraints.
Hope that clarifies it for you!
Regards,
Darini H.D
Link copied. Please paste this link to share this article on your social media post.