Cable termal constrait

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Cable termal constrait
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
laumarher
laumarher
Cadet

Posted: ‎2025-09-19 12:21 AM

0 Likes
3
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-19 12:21 AM

Cable termal constrait

How to resolve that warning?:

"Cable termal constrait (i2t>k2s2) is exceded at 10 ms, please check if circuit breaker energy limitation curve validates k2s2<i2t for short circuit value, otherwise please increase cable cross section value oh [PH]"

 

I have tried increasing the cable section and it does not solve the problem.

 

I attach a file, thank you

Attachments
Oficina_DNI_20250919.eac
Labels
  • Labels:
  • How to
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Darini
Lieutenant JG Darini Lieutenant JG
Lieutenant JG

Posted: ‎2025-10-30 10:27 PM

0 Likes
0
162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 10:27 PM

hi @laumarher  ,

thanks for the query!

this issue here is that Ecodial showed a “thermal constraint (I2t > k2S2) exceeded” warning for cables

This means that during a short-circuit, the energy passing through the cable (I2t) was higher than what the cable’s insulation and size could safely handle.

Reason:
The fault current at that point was around 12 kA, and the earlier cable size (1.5 – 10 sqmm) was too small to withstand that energy.

Workaround:
After increasing the cable size to 16 sqmm (Cu/PVC), the cable can now handle the short-circuit energy, and the warning is cleared.

so you might have tried to increase the CSA to 4 or 6sq.mm and that is not sufficient according to the constraints.

Hope that clarifies it for you!

Regards,

Darini H.D

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-09-19 07:48 AM

0 Likes
0
308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-19 07:48 AM

Hello @laumarher, thank you for your post, we'll come back to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Sumit_Kumar
Sumit_Kumar Cadet
Cadet

Posted: ‎2025-10-30 08:59 PM

0 Likes
0
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 08:59 PM

@Darini please have a look at it

Reply

Link copied. Please paste this link to share this article on your social media post.

Darini
Lieutenant JG Darini Lieutenant JG
Lieutenant JG

Posted: ‎2025-10-30 10:27 PM

0 Likes
0
163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 10:27 PM

hi @laumarher  ,

thanks for the query!

this issue here is that Ecodial showed a “thermal constraint (I2t > k2S2) exceeded” warning for cables

This means that during a short-circuit, the energy passing through the cable (I2t) was higher than what the cable’s insulation and size could safely handle.

Reason:
The fault current at that point was around 12 kA, and the earlier cable size (1.5 – 10 sqmm) was too small to withstand that energy.

Workaround:
After increasing the cable size to 16 sqmm (Cu/PVC), the cable can now handle the short-circuit energy, and the warning is cleared.

so you might have tried to increase the CSA to 4 or 6sq.mm and that is not sufficient according to the constraints.

Hope that clarifies it for you!

Regards,

Darini H.D

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore