Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Busbar vs Cable

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Busbar vs Cable
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
Canalis Busbar Trunking System

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
HarryCadman
HarryCadman Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-05 04:51 AM . Last Modified: ‎2022-01-25 11:50 PM

1 Like
0
4888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-05 04:51 AM . Last Modified: ‎2022-01-25 11:50 PM

Busbar vs Cable

Fire Prevention

Busbar Vs Cable

 

Cable presents several challenges to the installer. Among these is the need to terminate multiple cables in switchboards. With cable, entry holes must be drilled on-site, and particular care is needed to ensure accurate positioning of these holes and avoid the risk of swarf falling into the electrical connections, causing short circuits. Cable ladders would also need to be installed to support the cable during installation, as well as circuit protective conductors. These could require a dedicated team to set up. The cables would need to be tidied up, glanded into the switchboard and terminated. Each of these operations includes the risk of damage to the insulation, to the core itself, and bad termination that increases the risk of fire. In contrast, busway is much more straightforward. A single run of busway replaces several runs of cable, along Selecting conductors Correct conductor and overcurrent-protection sizing is critical in reducing electrical fire risks. Busways can help designers get around the electrical fire risks that conductors can pose. with associated cable trays. Busway also needs fewer fixings than the equivalent length of cable.

 

 

Busway temperature rises and short circuit withstand are known and independent of the installation, they are tested and certified according to IEC 61439-6 standards. In addition, coordination of the Schneider Electric circuit breaker and busways ensure an optimized sizing with perfect protection against short circuit conditions. Also, for high current circuits, multiple cables in parallel can lead to uneven distribution of currents and the risk of abnormal temperature rises. Installation standard IEC 60364- 5-52 Clause 523.7 recommends busbar trunking systems (busways) above four parallel cables. In France, this is mandatory, according to UTE C 15-105 chapter B.6.2.

 

Another major advantage of busbar is the use of tap-off units instead of a derivation box. These incorporate protective devices, which allow the busbar to feed other sub-circuits in the building. A variety of protective devices are available, including modular circuit breakers and molded case circuit breakers.

The rated performances are standard-compliant, irrespective of implementation, and the tap-off units are seamless to install and deliver high contact quality during aging. Mechanical protection of conductors significantly reduces the risk of insulation faults due to external factors, such as rodents, moisture, and pollutants. IEC 60364-4-42 2010 422.3 mentioned earlier, states that busbar need not be protected by 300mA RCDs in locations with special risk of fire, as they are not considered likely to cause a fire from insulation faults.

 

Please come back to see additional webinars, leaflets and information to help you decide on our busbar system and the benefits it brings of using cable.

Labels
  • Labels:
  • Products
  • Safety - Electrical Fire Prevention
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore