BMS Control of NSX MCCB's Fitted With Communicating Motors

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • BMS Control of NSX MCCB's Fitted With Communicating Motors
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All
Related Products
product field
Schneider Electric
ComPacT NSX, new generation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-06-30 01:37 AM . Last Modified: ‎2022-06-30 03:36 AM

0 Likes
5
3171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 01:37 AM . Last Modified: ‎2022-06-30 03:36 AM

BMS Control of NSX MCCB's Fitted With Communicating Motors

Good morning,

Is there a white paper/information details available on how to control NSX MCCB's which are fitted with communicating motor operators by the BMS/SCADA system?

We are seeing a number of projects which are requiring load shedding/re-close of devices by the BMS/SCADA system and it would appear to be a lot simpler to control this via either RS485 or TCP/IP connection than traditional wired I/O points.  

Labels
  • Labels:
  • Connectivity
  • Power Availability
  • Products
  • Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-06-30 02:06 AM

1 Like
4
3164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 02:06 AM

Hello Peter

You can find all information about Circuit Breakers With Communicating Motor Mechanism on this document page 56

 

BSCM and NSX cord are needed and you must to pass true communication devices from Enelin'X function to connect it to a Scada (see Page 149  on compact NSX catalogue)

 

 

 

 

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-06-30 02:06 AM

1 Like
4
3165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 02:06 AM

Hello Peter

You can find all information about Circuit Breakers With Communicating Motor Mechanism on this document page 56

 

BSCM and NSX cord are needed and you must to pass true communication devices from Enelin'X function to connect it to a Scada (see Page 149  on compact NSX catalogue)

 

 

 

 

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-06-30 04:21 AM

In response to Gregoire_Brun
1 Like
3
3147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 04:21 AM

Thank you Gregoire, that is a great help.

 

Just need to convince consultants now that it can be done...

 

Best regards,

 

Peter Hall.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-06-30 07:46 AM

In response to Peter_Hall
0 Likes
2
3129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 07:46 AM

We imagine to create for the futur a 24v DC version for communicative Motor mechanism, should be a needed for you ? 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-06-30 08:26 AM

In response to Gregoire_Brun
0 Likes
1
3124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-30 08:26 AM

That could be interesting.

 

Although we are seeing enquiries at present that open the MCCB's on loss of supply to the busbars. Therefore a 230VAC UVR is needed. If a 230VAC UVR is used it would be quite simple to supply the motor from this supply.

 

A 24VDC option would need a separate DC supply bringing into the panel as the ULP supply could not be used as it is limited in its rating. 

 

A tricky one. On one hand it would be convenient, but in this application maybe the 230V supply is just as convenient?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-07-01 01:32 AM

In response to Peter_Hall
0 Likes
0
3107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-01 01:32 AM

You are right,

It depend if they use micrologic 5-6-7 with external DC Supply or not.

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of