Adjustable trip CB marked for continuous operation at 80%
  • Power Distribution IEC
  • Adjustable trip CB marked for continuous operation at 80%
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Posted: ‎2020-12-03 12:08 PM
2
2472
How does adjusting the trip on a circuit breaker affect the marked 80% continuous operation rating? See CEC C22.1-18 8-104 6). Ie. is the trip adjustment a percentage of the 80% continuous rating?
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
Posted: ‎2020-12-07 05:25 AM
1
2451
In Schneider Electric / Square D range of adjustable circuit breaker there is no link between the setting of overload protection "Ir'" and the 80% or 100% rating capability of the circuit-breaker.
Selecting 80% standard rating or 100% rating is more a question of enclosure design due to thermal dissipation for continuous load, rather than a setting question that is linked to the ampacity of the protected circuit.
Masterpact circuit breakers  and PowerPact M,P, R frames are designed for continuous operation at 100% of their current rating, and the setting of Ir is given in % of "In" the rated current of the trip unit.
PowerPact  B, H,J, L ranges are offering "80% rated"  or "100% rated" references. Both will have the same trip units with overload setting in Amps.  A 80% rated should be adjusted up to 80% of the rating when used with a continuous load but can be ajdusted up to 100% with non continous load.
Does it answer your question ?
Regards
MathieuGuillot
Lieutenant
1
2452
Regards
Posted: ‎2020-12-07 11:58 AM
In response to MathieuGuillot
Hello Mathieu
Thank you for taking the time to respond to my question. This is crystal clear.
Best regards,
Brian