Pada software Vijeo Designer Basic apakah saya dapat menambahkan driver PLC lain?
Pada kasus saya, saya ingin menyambungkan PLC Siemens S7-300 dengan kabel MPI Adapter, tetapi pada vijeo designer basic tidak memiliki driver tersebut.
Mohon di bantu untuk permasalahan tersebut.
Terima kasih.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
pada 2021-06-20 07:48 PM
Halo pak,
Bapak bisa tambahkan di IO manager,
Klik kanan "...New Drive"
Manufacturer Pilih, Siemens AG
Kemudian Pilih Driver, SIMATIC S7 MPI/PPI
dan terakhir Pilih, S7-300/400 series.
Semoga membantu,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
pada 2021-06-20 07:48 PM
Halo pak,
Bapak bisa tambahkan di IO manager,
Klik kanan "...New Drive"
Manufacturer Pilih, Siemens AG
Kemudian Pilih Driver, SIMATIC S7 MPI/PPI
dan terakhir Pilih, S7-300/400 series.
Semoga membantu,