Bagaiman Cara Pengisian Parameter PID

PLC Club Indonesia

Wadah diskusi seputar PLC,HMI, SCADA dan semua hal seputar otomasi pada proses industri, baik mengenai hal teknis, informasi terbaru dan juga seputar bisnis. Forum ini terbuka unutuk semua system integrator industrial di Indonesia

gwynbleidd
Crewman
Crewman
0 Likes
1
386

Bagaiman Cara Pengisian Parameter PID

Bagaimana cara mengisi Kp, Ti, Td pada PID?

misal paramater yang dapatkan Kp=20, Ti=90, Td=45 bagaimana memasukkan ke dalam %MWxx nya apakah perlu dikali dulu? 

Mohon bantuannya, Terima kasih.Screenshot 2021-08-16 181005.png

Tags (2)
1 Reply 1
endr0kho
Crewman Crewman
Crewman
0 Likes
0
344

Re: Bagaiman Cara Pengisian Parameter PID

Tidak perlu dikali, tanda x dimanual tersebut mewakili satuannya, jadi kalau kita masukkan Kp = 10 artinya dalam kalkulasi PID yang dihitung adalah 10x0,01s = 0,1s. begitu juga untuk Ti dan Td

CMIIW