New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
what is the minimum pulse width that the BMXDDI1602 can detect?
Modicon PAC Forum
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-0801:00 AM
Hello Bianca,
You have to take into account the response time of the module itself (3-7 mS) but more important the total cycletime of your application in the CPU. If the CPU cycletime is 10 mS, the minimum pulsewidth to detect is 10ms, but better would be 20mS (2* the PLC cycletime), just to be sure that the cycletime is less than your pulswidth (Nyquist-theorem). If the DDI module is located in a remote IO drop, you might need to take the Drop process time, network timing and Network update time (RPI) into account. Basically if you know what the minimum pulsewidth is, and you know what your CPU cycletime is you can make a rough estimate if you can use a standard DDI or you need a High speed module.