Verifying Project File Build Signature

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Verifying Project File Build Signature
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
Adrian_Lee
Ensign Adrian_Lee Ensign
Ensign

Posted: ‎2021-10-25 05:08 AM . Last Modified: ‎2021-10-25 05:10 AM

0 Likes
1
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 05:08 AM . Last Modified: ‎2021-10-25 05:10 AM

Verifying Project File Build Signature

In the Control Expert function block library there is a PRJ_VERs function block that lets you read the 'Build Signature' of a project.

This signature appears to be part of the same signature number that shows up in 'PLC Screen' -> Information tab under 'Application -> Identification' when you are connected to a PLC running a project.

 

My questions are:

  1. How can one obtain the build signature of a project file (.STU) in Control Expert without first transferring it into a PLC?
  2. Is it possible to read the build signature of a project file without using Control Expert at all? There are some similar looking numbers in STATION.CTX file but not sure if that's a reliable approach to take.

 

I'd like to script a way of recording and verifying PLC project file build signatures to ensure they aren't tampered with. There have been numerous vulnerabilities related to crafting malicious project files and opening them in Control Expert or downloading to PLC. Would be good if there was a reliable and scalable method of recording signatures and verifying integrity of project files.

Labels
  • Labels:
  • 06. EcoStruxure Control Expert
  • Tags:
  • cybersecurity
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Adrian_Lee
Ensign Adrian_Lee Ensign
Ensign

Posted: ‎2022-01-11 03:40 PM . Last Modified: ‎2022-01-11 03:45 PM

0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-11 03:40 PM . Last Modified: ‎2022-01-11 03:45 PM

For #1, the project file (.STU) can be unzipped, and you can find the STATION.CTX which contains the build signature

 

Got some information back from support regarding #2

The version application signature is composed of 4 values -> CID-MID-AID-LID and you can find bellow the description of each one of the values:

CID - Creation ID: Random number generated when an application is created. The number remains a constant.

 

MID - Modification ID: Random number generated on each application modification and rebuild, either partial or global. When an application is created, MID = CID.

 

AID - AutoModification ID: A new random value generated for AID by the PLC after one of the following minor modifications to the application:

  • a Control Expert request to modify %KW
  • a P_Unit request that performs a save_param request or replaces init value

When an application is created or built in local mode, AID = 0.

 

LID - Layout ID: Random number generated after a modification of the variable layout. LID does not change as a result of a runtime change either adding or deleting a data block. LID changes only on when the global rebuild of the application.​
LID addresses the needs of Hot Standby. It permits the transfer of a memory block from the primary PLC to the standby so that application variables (excepted for deleted or new ones) exist at the same location
LID = CID = MID when the application is created.

 

https://www.se.com/ww/en/faqs/FA371483/

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Adrian_Lee
Ensign Adrian_Lee Ensign
Ensign

Posted: ‎2022-01-11 03:40 PM . Last Modified: ‎2022-01-11 03:45 PM

0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-11 03:40 PM . Last Modified: ‎2022-01-11 03:45 PM

For #1, the project file (.STU) can be unzipped, and you can find the STATION.CTX which contains the build signature

 

Got some information back from support regarding #2

The version application signature is composed of 4 values -> CID-MID-AID-LID and you can find bellow the description of each one of the values:

CID - Creation ID: Random number generated when an application is created. The number remains a constant.

 

MID - Modification ID: Random number generated on each application modification and rebuild, either partial or global. When an application is created, MID = CID.

 

AID - AutoModification ID: A new random value generated for AID by the PLC after one of the following minor modifications to the application:

  • a Control Expert request to modify %KW
  • a P_Unit request that performs a save_param request or replaces init value

When an application is created or built in local mode, AID = 0.

 

LID - Layout ID: Random number generated after a modification of the variable layout. LID does not change as a result of a runtime change either adding or deleting a data block. LID changes only on when the global rebuild of the application.​
LID addresses the needs of Hot Standby. It permits the transfer of a memory block from the primary PLC to the standby so that application variables (excepted for deleted or new ones) exist at the same location
LID = CID = MID when the application is created.

 

https://www.se.com/ww/en/faqs/FA371483/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of