TSX AEY414 Replacement

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • TSX AEY414 Replacement
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All
Related Products
product field
Schneider Electric
Modicon Quantum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-03-11 01:57 AM

0 Likes
11
3835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-11 01:57 AM

TSX AEY414 Replacement

Dear All,

TSX AEY414 was installed on a machine which became faulty and I installed new same module.

 

Problem is that new module don't show any error only RUN indication is ON. but HMI is showing 0 values from that module

 

I think PLC is not reading the values of new module

 

can anyone help me what may be the reason?

waiting for reply

 

Thanks

Shoaib

Labels
  • Labels:
  • 00. Read me first
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-03-11 02:13 AM

0 Likes
10
3826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-11 02:13 AM

Hello Shoaib,

 

Please check if the input signals are available. Depending on the signal type connected (+/-10V or mA) you should be able to measure some voltage. If thermocouples are connected this might be more difficult.

 

If this doesn't help, contact your local support/service team.

 

Br

Rene

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-03-11 02:17 AM

In response to RoozeeR
0 Likes
9
3824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-11 02:17 AM

Dear Sir,

 

I have checked the voltage levels and 2-3 volts are present. is it cab be due to SV/PV or RL difference?

 

waiting for reply

 

Thanks

Shoaib

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-03-11 02:21 AM

In response to ghulamshoaib
0 Likes
8
3818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-11 02:21 AM

Hello Shoaib,

 

Contact your local support/service team, they can help.

 

 

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-04-21 12:23 AM

In response to RoozeeR
0 Likes
7
3686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-21 12:23 AM

Hello,

 

Can I check the module by placing it to some other slot of the same rack? 

to place the module on other slot, do I need to make any changes in hardware configuration of the PLC program or not?

 

please reply

 

Thanks

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-04-21 12:58 AM

In response to ghulamshoaib
0 Likes
6
3678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-21 12:58 AM

Hello,

When you place the module in another slot, you have to make changes to the hardware configuration (in software).

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AlastairF
AlastairF Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-04-21 01:24 AM

In response to RoozeeR
0 Likes
0
3673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-21 01:24 AM

Re-working module addresses after moving a module depends on the programming environment.

If you are using Control Expert then a drag and drop of the module to another slot will automatically update the associated variable addressing. Cut and Paste does not move the addresses to the new slot.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-04-21 06:42 AM

In response to RoozeeR
0 Likes
4
3666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-21 06:42 AM

if I will change the slot, should I also need to change the addresses?

 

which software should I use ? unity Pro or PL7?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

KenPlimmer
KenPlimmer Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-04-21 07:03 AM

In response to ghulamshoaib
0 Likes
3
3662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-21 07:03 AM

Hello,

 

the software which you will need to change the configuration in the TSX57 will depend on the CPU reference. Earlier systems would use PL7 Junior / Pro, updated systems or later installations will require Control Expert for Unity applications.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-05-24 10:30 PM

In response to KenPlimmer
0 Likes
2
3477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-24 10:30 PM

If I want to test the module TSXAEY414 on some other slot of the same rack, Do I need to make changes in Hardware configuration of the PLC program?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

AlastairF
AlastairF Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-05-30 01:38 PM

In response to ghulamshoaib
0 Likes
1
3434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-30 01:38 PM

Yes, you need to add the module type into the spare slot so the CPU can give the module its configuration.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ghulamshoaib
Ensign ghulamshoaib
Ensign

Posted: ‎2021-06-14 04:28 AM

In response to AlastairF
0 Likes
0
3332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-14 04:28 AM

Dear All, 

Can I use TSXPCX3030 cable for comunicating with CPU P57103?

As I don't have TSXUSB485 cable

 

Waiting for reply

Thanks

Shoaib 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of