Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Retain last counter value before power fail

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Retain last counter value before power fail
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Modicon M580
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
dty.jo
dty.jo Explorer
Explorer

Posted: ‎2025-02-03 02:05 AM

0 Likes
2
2560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-03 02:05 AM

Retain last counter value before power fail

As I find solution on internet they advise to uncheck initialize %MW on cold start and cold start then value will be retain but as I tested, I uncheck them and provide the counter value (output) to address %MW10 then reset power. After PLC back to online value set to 0.

 

Could you please recommend how to retain last value. (M580 P4040s)

dtyjo_0-1738576984121.png

dtyjo_1-1738576994518.pngdtyjo_2-1738577004314.png

 

 

 

  • Tags:
  • Control Expert
  • EcoStruxure Control Expert
  • english
  • m580
  • modicon
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
GeoffChisholm
GeoffChisholm
Troubleshooter

Posted: ‎2025-02-09 01:17 PM

0 Likes
0
2472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-09 01:17 PM

I would suggest rather than using a CTU instruction just use some code that increments a value in a located variable (%MW), then use the retain value on cold start option. If you had multiple counters that needed to be retentive then I would develop a custom DFB where the count value was an In/Out variable and that variable was connected to a located variable (%MW)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Bosswaffle
Bosswaffle
Troubleshooter

Posted: ‎2025-02-09 09:43 AM

0 Likes
0
2483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-09 09:43 AM

@dty.jo, unfortunately in this scenario CV is an output, so on first execution of the program cycle it'll be written as the output of the CTU (zero in this case), regardless of the initial value of variable.

 

You might try a CTUD FB. With this block, you could move the CV output into a unlocated variable that is connected to the LD input of your counter. Then use then the warm startup bit (%S1) to load in the saved value, I uses a SEL FB with the warm startup bit so that I can still us the PV as normal.

 

The benefit of this method is that you can leave the 'initialize %MW on cold start' in which ever state you prefer.

 I like it checked personally. If you keep it unchecked you could use a located variable instead of a unlocated one, as I suggest above.

 

The downsides are that you might not always want this behavior? There are probably some edge cases where it gets weird, but I can't think of any right away.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

GeoffChisholm
GeoffChisholm
Troubleshooter

Posted: ‎2025-02-09 01:17 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-09 01:17 PM

I would suggest rather than using a CTU instruction just use some code that increments a value in a located variable (%MW), then use the retain value on cold start option. If you had multiple counters that needed to be retentive then I would develop a custom DFB where the count value was an In/Out variable and that variable was connected to a located variable (%MW)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore