Reading input register 3x from third party modbus
Modicon PAC Forum
Select a Country
  • Industrial Automation
  • Modicon PAC Forum
  • Reading input register 3x from third party modbus
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
Modicon Quantum
Back to Modicon PAC Forum
Posted: ‎2022-01-17 11:37 AM
5749
Hi All
I am trying to read from input register 3x of skf analyst software using Quantum PLC ( 140 CPU 652 60 & 140 NOE 771 10)
I tried MBP_MSTR but it didn't work.
Any ideas please. Please feel free to suggest other PLCs (m340, m580,etc) as well if quantum doesn't support reading 3x from 3rd party
Ali
  • 00. Read me first
Replies 8
bricesumner
bricesumner
Explorer
Posted: ‎2023-12-13 12:05 PM
Hi Ali,
Did you get this figured out?
If not, a couple of hints with the Quantum:
  • There is a register offset (requesting register %M1 gets you %M2)
  • The request in the data buffer follows the Modbus standard (attached see section 6.4 of Modbus Application Protocol)
ciupol
ciupol
Mentor
Posted: ‎2023-12-15 05:26 AM
MBP_MSTR can read only 4x registers. To read 3x registers you can use READ_VAR.
GeoffChisholm
GeoffChisholm
Troubleshooter
Posted: ‎2023-12-19 08:40 PM . Last Modified: ‎2023-12-19 08:50 PM
5256
Read_Var would be easier but this is not available in Quantum, and Read_Reg which is the quantum function does not read input registers.
you can use the MBP_MSTR function only you have to use mode 15 to send a Modbus Request and set the Modbus function code to read input registers. It is possible, it is just complicated. The help in Control Expert will help. The Modbus Function code you need is 04 to read input registers.
bricesumner
bricesumner
Explorer
Posted: ‎2023-12-20 07:16 PM
In response to GeoffChisholm
Yes, you’re right. I just helped someone getting the read and write to coils working.
The hardest part is getting the bytes setup in the words properly. It’s easier to view everything in hexadecimal.
I also found that it made more sense to write everything out in decimal, ignoring the bytes, then converting to hexadecimal and adding the extra bytes (using the modbus manual). Then combining everything into the words. I can send examples on Tuesday.
bricesumner
bricesumner
Explorer
Posted: ‎2023-12-26 08:02 AM
In this example I'm writing to coils (%M):
From the Modbus Application Protocol manual this is the structure of my request (write multiple coils):
Function Code: 1 byte
Starting Address: 2 bytes
Quantity of Outputs: 2 bytes
Byte count: 1 byte (value is N*)
Outputs Value: N* bytes
Also from the manual N* is number of registers divided by 8 and rounded up.
In my application I have 2 registers I'm writing to starting at register 17 so my request is as follows:
Function code: 15
Starting address: 16 (0 based addressing)
Quantity of ouptuts: 2
Byte count: 1 (2÷8=0.25 but rounded up is 1)
Outputs value: 3 (turn both outputs on: 3 is 0000 0011 in 8 bit binary)
Convert to hex to make the bytes easier to read:
Function code: F
Starting address: 10
Quantity of outputs: 2
Byte count: 1
Outputs value: 3
Adding padded 0's to make all of the bytes is use visible:
Function code: 0F
Starting address: 0010
Quantity of outputs: 0002
Byte Count: 01
Outputs value 03
Combining them into a long stream the whole request looks like:
0F001000020103
Breaking up into the WORDS used in Control Expert and adding extra 0's to complete the last word:
0F00 1000 0201 0300
So using the example in control expert for MBP_MSTR operation code 15 the first part of my Data Buffer array should look like:
Buffer[1]: 16#0F00
Buffer[2]: 16#1000
Buffer[3]: 16#0201
Buffer[4]: 16#0300
My Control Array should look like:
Control[1]: 15
Control[2]: 0 (system reserved for error code on response)
Control[3]: 11 (the example had the buffer as a size 11 array)
Control[4]: 5 (I'm only using 4 registers, but I'll give myself some padding and since my array is size 11; then 2*5=10 so I won't go past the length of my array.
Control[5]: 16#0400 (first byte is the slot of my NOE, second byte is a lookup index (i.e. if you were using a bridge mux or a gateway))
Control[6]: 192 (next 4 are the IPv4 address, my example is 192.168.0.1)
Control[7]: 168
Control[8]: 0
Control[9]: 1
Control[10]: 7 (Length of request in bytes: 0F 00 10 00 02 01 03)
Control[11]: 0 (system reserved length of response)
So the rest of my Buffer is as follows:
Buffer[5]: 16#0000 (Padding from Control[4])
Buffer[6]: 16#0000 (First part of response)
Buffer[7]: 16#0000 (Second part of response)
Buffer[8]: 16#0000 (Third part of response)
Buffer[9]: 16#0000 (Unused)
Buffer[10]: 16#0000 (Unused)
Buffer[11]: 16#0000 (Unused)
From the Modbus Application Protocol the response is as follows:
Quantity of outputs 2 bytes
So if my device is following the Modbus standard my buffer should look like the following to mirroring my request:
Buffer[6]: 16#0F00
Buffer[7]: 16#1000
Buffer[8]: 16#0200
arvind121
arvind121
Explorer
Posted: ‎2024-05-13 03:36 AM
4782
hi all im trying to read input variables from a modbus slaves device, i have tried to read variables using MBP_MSTR Function block but im not able to read variables, someone please refer the attached images and help me on this! thanks
bricesumner
bricesumner
Explorer
Posted: ‎2024-05-15 06:18 AM
In response to arvind121
Should probably start this as a new post rather than hopping on someone else's, but a few things:
  • With a M580 why are you using MBP_MSTR? Read_Var can read input registers
  • As I think you've found, the enable pin has to be pulled high until the action completes, the attached screenshot is how I'd recommend performing the action.
  • In your MBP_MSTR_CONTROL variable you have a value of 4 in the first location in the array which is Clear Local Statistics, not Read/Write Data (23) nor Send Modbus Request (15).
  • Your MBP_MSTR_CONTROL variable is an array of 0 to 10, I think the block requires a 1 to 11.
  • What is in your MBP_MSTR_DATA variable? This is a buffer that has the heart of your request along with the response from the slave device.Screenshot 2024-05-15 061046.png
MatthewM
MatthewM
Mentor
Posted: ‎2024-05-15 12:11 PM
@arvind121 Consider using a READ_VAR with that hardware.