Dear Commmunity
I have the project that use PLC Modicon M580 connected to Easergy P5F30 relay via Iec61850 protocol thought NOP0300 I/O card. we met 2 from 30 pcs of the relay don't updated value when real measurement or BI at relay has changed. Could you please advised procedure to investigation or fixing them.
Activity we done below.
1. Use IED scout monitor, the value as changed as real value at P5F30
2. Down load new CID file to P5F30
3. Disconnecetd and connected UTP cable to P5F30, the value that monitor at PLC has changed but then they still this value
Thank you
Maitree R.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-28 01:38 AM
Hi @Maitree_ri,
Check my comments below:
My understanding is that you have 30s P5 relays communicating with the BMENOP0300 module, and you are facing issues with two of them. Is that correct?
I would advise you to start the investigation with the following:
The below snapshot is just for your reference for polling and reporting control blocks "CMD" and "status" inside the DDT.
I hope the above comments provide help at least to initiate the investigation.
Best Regards,
MWS
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-31 07:08 AM
Hi @Siddiqui
Thank for your advised please find my reply as below.
Yes I mean we have P5F30 30+ pcs connected to BMENOP0300 modules . And I attached system architecture as attached. (As attached have P5M30 10+ pcs)
1. As we are checked, the freshness status value is 1.
2. Yes, I confirmed they are same CID files at P5 relay and BMENOP0300 module.
3. I'm not sure that's the meaning of the polling method. As the attached picture shows, the polling status shows failed after being sent.cmd, but the others are normal.
4. Is it same as 3.? Or do you mean check error at P5 relay, please advised.
5. How to checked which way in IED scout? polling or report?
6. I attached logic file for review.
If you need more information, do not hesitate to request from me.
Thank you.
Maitree R.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-31 03:43 PM
Hi@Maitree_ri,
Thank you for sharing more details.
I checked your application. You have configured five P5 relays inside the NOP module and are reading the data from IEDs using the polling method. As you mentioned, the freshness status value of all five IEDs is 1. Please confirm this.
For the IED SW05_IR1_P5F, you are facing an error on the polling command status. Have you been facing this error since the start of the polling command? OR does it work fine for a few polling commands, and then it starts giving this error status?
I suggest the following: In your polling trigger logic, please verify the polling command status feedback for the given polling command and make sure you get the successful feedback status before initiating the following polling command.
Maybe you are polling too fast at every 200ms? But you can verify this while doing the test with IEDSCOUT, as explained later on in this comment.
You can convert the Polling command status into binary and then segregate the low and high bytes to understand the status clearly, as shown in the snapshot below.
The snapshot below explains the polling command status register. For example, the CMD is triggered with the value 1. Bit 0 of the low byte of the command status register is also equal to 1. The High bytes of the command status registers show that the command is successfully executed with bits 7 and 6 equal to 01.
Please refer to the BMENOP0300 module user guide for a detailed explanation of status registers.
You can access the TVDA document from the following link. It might help you better understand the BMENOP0300 module and the basics of the IEC 61850 data exchange mechanism.
Connect Modicon M580 to an IEC61850 Network
From the IEDSCOUT, if you drag and drop the Data Object (DO) into the "Activity Monitor" Windows screen, you can also configure the polling interval, which is set to 1 second in the snapshot below.
The following DOs from the IR1_P5F relay you are reading through the polling method inside the BMENOP0300 module, you can use IEDSCOUT and drag all those DOs and perform the test to make sure you are able to poll all the information from this P5 without getting any errors. From here, you can start the investigation.
I am on vacation, so I did not go through the shared architecture, but it would be great if you could provide a simple explanation of the connection between the NOP module and the IEDs.
I hope the above comments help start the investigation. Please share the outcome of the IEDSCOUT test, and we'll see where it leads.
Best Regards,
MWS
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of