Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-27 07:26 AM
Hi everybody.
We are working on a project using M580S with HSBY configuration. Kindly refer to attached system architecture for more details (M580S Config.jpg).
We noticed the status on Control Expert screen is showing A-RUN_PRIM / B-STOP / EQUAL. More details can be referred to attached video and pictures.
Kindly guide us on how to achieve B-RUN_STANDBY. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-29 03:31 AM
A few things to check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-29 03:31 AM
A few things to check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-30 07:39 PM
Hi @Trinxs1,
Thank you very much for your guidance. We managed to solve the issue.
Yes, the remote IO extension racks come with terminators. Now we are getting A-RUN_PRIM / B-RUN_STBY / EQUAL. Thank you again.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.