Posted: 2025-06-27 07:26 AM
Hi everybody.
We are working on a project using M580S with HSBY configuration. Kindly refer to attached system architecture for more details (M580S Config.jpg).
We noticed the status on Control Expert screen is showing A-RUN_PRIM / B-STOP / EQUAL. More details can be referred to attached video and pictures.
Kindly guide us on how to achieve B-RUN_STANDBY. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-29 03:31 AM
A few things to check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-29 03:31 AM
A few things to check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-30 07:39 PM
Hi @Trinxs1,
Thank you very much for your guidance. We managed to solve the issue.
Yes, the remote IO extension racks come with terminators. Now we are getting A-RUN_PRIM / B-RUN_STBY / EQUAL. Thank you again.
Link copied. Please paste this link to share this article on your social media post.