Posted: 2024-09-30 05:45 AM
I'm finding conflicting info on using a M340 with the 1002 redundant PS rack. I have the M340, and a NOE module in the rack. Customer wants to use the redundant power supply rack. My understanding is that everything will work as is but the monitoring/diagnostics for the power supplies cant be read by the M340. Can anyone clarify?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-04 01:41 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-30 03:26 PM
For the diagnostics to be displayed the module must be used in a redundant rack with an M580 CPU. The M340 CPU will not support the function block that is used to provide the diagnostics.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-02 05:31 AM
Thank you!! That being said, I will use the relay contacts on the PS to monitor for failure. Otherwise, will the M340 work? I can configure the dual ps rack, M430 and the NOE and build the project with no errors.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-04 01:41 AM
It will work.