M340 Modbus command to read input registers
Good evening,
I have a PLC P34 1000 and communicate with a flow converter through modbus rtu . but the data i need to read exist on input registers and the manual of converter telling that you have to use command 4 as known but when i'm using read_var the communication halt after a while and the data is not recognized because the data type sent is floating.
by the way i read the holding registers and everything is ok.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-3006:38 AM
The READ_VAR function should be able to read input registers as long as you define the obj type as %IW. The function code to read %IW is 4 .
You mention " the data is not recognized because the data type sent is floating.":
1: does this mean that the input data you read is a 32-bit floating point (real) data? In that case you should adjust the read length to 2 (registers= 32 bits).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-3006:38 AM
The READ_VAR function should be able to read input registers as long as you define the obj type as %IW. The function code to read %IW is 4 .
You mention " the data is not recognized because the data type sent is floating.":
1: does this mean that the input data you read is a 32-bit floating point (real) data? In that case you should adjust the read length to 2 (registers= 32 bits).