M172 with TM172 Display and internal Temperature Sensor

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M172 with TM172 Display and internal Temperature Sensor
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Mick0275
Lieutenant | EcoXpert Master Mick0275 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-12-15 03:32 PM

1 Like
7
3115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-15 03:32 PM

M172 with TM172 Display and internal Temperature Sensor

Hi Folks, 

 

I have couple programs running with communication from M172 to the TM172DCLWTH HMI, i can easily access the plc "status variables" from the HMI to show statuses on the screen. 

Now the idea is to use the internal temperature sensor of that TM172 HMI, i know the variable in the display where the temperature value gets written into but i am not able to use that temperature variable in my PLC program. 

I just cannot drag and drop the variable from the "HMI Vars and Parameters" window in my ST programming window. 

When I type that variable in my program then I will get an error when I compile the program. 

Is there a way to have access the HMI variables in the M172 controller and if yes how can I achieve that? 

 

Thanks alot in advance. 

 

Michael

  • Tags:
  • english
  • M172
  • modicon
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2021-12-27 07:31 AM

0 Likes
2
3096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-27 07:31 AM

Hi,

 

I guess you are using the TM172 Display as modbus master of the M172 PLC.

If this is the case, I suggest you define a R/W Status Var on M172 PLC and write on it periodically from the PLC of the TM172 Display the value of the temperature sensor.

 

TM172 Display has target blocks which allows to write modbus messages from the Programming section.

 

BR,

Federico

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Mick0275
Lieutenant | EcoXpert Master Mick0275 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-12-27 02:53 PM

In response to FedericoM
0 Likes
1
3091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-27 02:53 PM

Hi @FedericoM ,

 

thank you for your respond. 
yes the TM172 is connected via mod is master. 
i cannot access target variables in the plc from the display. I can use the target variables in the display editor but that doesn’t work. 
i need to somehow write the temp variable from the plc in to the plc. 
can you make an example please what you mean? 
Your help is very appreciated. 

regards, 

 

Michael

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2021-12-27 11:52 PM

In response to Mick0275
1 Like
0
3083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-27 11:52 PM

Hi,

 

try to check the examples and powerpoints available at this link:

 

https://schneider-electric.box.com/s/fqho8wmbqyfk5n4ne103ydqmym1g4yw4

 

In the Fan Coil control example, in the Programming part of the TM172DCL project you can find a small program which writes some data from TM172DCL to M172.

 

At this link:

 

https://schneider-electric.box.com/s/76vujqoan6q4nof88ju8i0peue5jek3b

 

you can find a full project of TM172DCL used as thermostat, in this case TM172DCL is a modbus slave. It means you have to implement modbus master on M172 and read/write what you need from TM172DCL.

If you prefer a solution like this one (it allows to connect several M172DCL to a M172), check also the manual with the table of all the available modbus registers on the thermostat.

 

Regards,

Federico

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-01-02 11:23 PM

0 Likes
3
3069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-02 11:23 PM

Hi,

How is you configuration? You use a TM172P as controller and a TM172DCL as HMI?

If yes is the HMI Modbus RTU server or client?

If the HMI is server you could find the temperature on Modbus register 8208

If the HMI is client you need to write the value manualy down to the TM172P via target block sysMbMRTU_FC6.

 

best regards

  • Tags:
  • english
  • ESME HVAC
  • M172
Reply

Link copied. Please paste this link to share this article on your social media post.

Mick0275
Lieutenant | EcoXpert Master Mick0275 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-01-03 02:17 PM

In response to Bastian_Schmitz
0 Likes
2
3061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 02:17 PM

Hallo @Bastian_Schmitz, 

 

Yes i have have a TM172DCL connected to a TM172 via Modbus Master. 

Can you make a example how I could read that Modbus register 8208? 

I got thrown in the cold water and need to make it work. (Wurde ins kalte Wasser geschmissen) 

Your help is very much appreciated. 

Thank you. 

 

Regards, 

 

Michael

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-01-03 10:43 PM

In response to Mick0275
0 Likes
1
3056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 10:43 PM

Hello,

In that case you need to define on the TM172P a Status Variable which is set to read and write ability(Default) like explained from @FedericoM before.

 

After that you need to create a Programm which is aligned to the background task in the programming tab.

In this programm you need to use the Target block sysMbMRTU_FC6.

You could see here an example

zzmodbus.PNG

The functionblock need as input the follow information

addr      Modbus RTU address of the slave controller (a.e. 1 )
base    Modbus register address were you want to send your data
object  The value which you want to write
polling time Polling time in [ms]
timeout Timeout in [ms]
waitBeforeSend time in [ms]to wait before send

 

You could find this information also in the FB description.

  • Tags:
  • english
  • ESME HVAC
  • M172
Reply

Link copied. Please paste this link to share this article on your social media post.

Mick0275
Lieutenant | EcoXpert Master Mick0275 Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-01-17 11:53 AM

In response to Bastian_Schmitz
1 Like
0
3015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 11:53 AM

Hello @Bastian_Schmitz and @FedericoM 

 

thank you for your help, i made it work. 

I had to create a poll timing routine else the HMI would have a to low response time and was nearly impossible to operate it. 

Now I can read the HMI's internal Temperature and Humidity sensor. 

Really appreciated all your help and thank you for being so supported, the world need more people like you. 

Thanks. 

 

Regards, 

 

Michael 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of