Limit number of DIO devices under a DIO Main Ring

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Limit number of DIO devices under a DIO Main Ring
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
keithkcchan
Ensign keithkcchan Ensign
Ensign

Posted: ‎2020-05-26 07:49 PM

0 Likes
13
10759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 07:49 PM

Limit number of DIO devices under a DIO Main Ring

What is the limit on number of DIO devices by utilize HSBY M580 on board DIO ports?

What about the limit if using BMENOC0321 on the HSBY M580 Racks? 

  • Tags:
  • DIO number limit
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2020-05-28 02:23 AM

2 Likes
5
10718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-28 02:23 AM

The previous answers are all correct. Knowing the maximum, you have to consider multiple items:

 

1: Maximum supported DIO devices:

HSBY CPU: 61 (max = 64, 3 are reserved for Ethernet/IP local slaves)

BMENOC0321: 112 (max = 124, 12 are reserved for Ethernet/IP local slaves)

 

Be aware that connecting DIO devices direct to the device ports of a HSBY CPU might not work as the CPU device ports have a VLAN active, which might not be supported by the device. To overcome this issue, use external switches or use BMENOS0200 switch in the CPU racks.

 

2: Maximum supported input/output size

HSBY CPU: 4Kbyte IN + 4Kbyte out (see previous answers)

BMENOC0321: 4Kbyte IN + 4Kbyte out (see previous answers)

Basically this means that the amount of data communicated is DIO device type dependent. You have to calculate the amount of data each device is communicating + take the overhead into consideration. I use to create some configuration and see what the data is used for each specific device type.

 

3: Maximum communication bandwith of an interface

HSBY CPU: 15000 packets

BMENOC0321: 5500 packets

The amount of packets is depending on the configured RPI (Repeat Packet Interval / Repeat Rate / update rate). For example when you define 100 devices with an RPI of 10 mS, will result in minimal 2(Read+write) * (1000/10) * 100(devices) = 20.000 packets. Solution will be to decrease the RPI for some/all devices, to keep the amount of packets between the limits.

 

4: Physical network limitation

When using a RSTP ring functionality, the limitation is to have max. 40 device within a ring. As  both CPU's count as a RSTP device, this limits the amount of DIO devices in a ring to 38. This imitation comes from fixed RSTP parameter settings in Schneider Electric DIO devices with RSTP functionality enabled (ie Modicon STB, Altivar Process). To overcome this limitation you can create a network star (using switches) or create multiple network rings (also by using switches) 

R.Roozee
Sr Solution Architect (SAE Master)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Michael_Chan
Commander Michael_Chan Commander
Commander

Posted: ‎2020-05-26 09:24 PM . Last Modified: ‎2020-05-26 09:37 PM

1 Like
3
10754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 09:24 PM . Last Modified: ‎2020-05-26 09:37 PM

A HSBY system with a DIO ring can be constructed using

  • BME NOS 0300 module. The CPU alone scans up to 64 DIO devices.
  • One or more BME NOC 0301/11 modules to scan up to 128 devices.

DIO devices cannot be connected to the Remote I/O network. Connection to RIO main ring is possible through the service port of a CPU or a CRA adapter module, eNOC, eNOS Ethernet network option switch or a Modicon Switch (DRS).

CPU DIO Limit.png

Michael Chan Kum Yuen
Reply

Link copied. Please paste this link to share this article on your social media post.

Michael_Chan
Commander Michael_Chan Commander
Commander

Posted: ‎2020-05-26 09:32 PM . Last Modified: ‎2020-05-26 09:37 PM

In response to Michael_Chan
1 Like
2
10749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 09:32 PM . Last Modified: ‎2020-05-26 09:37 PM

The BME NOC 0321 control network module provides support for I/O scanning using EtherNet/IP and Modbus TCP.

NOTE: The maximum I/O scanning capability for a BME NOC 0321 module is 5,500 packets per second.

NOC0321 Limits.png

Michael Chan Kum Yuen
Reply

Link copied. Please paste this link to share this article on your social media post.

Michael_Chan
Commander Michael_Chan Commander
Commander

Posted: ‎2020-05-26 09:36 PM

In response to Michael_Chan
1 Like
1
10745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 09:36 PM

 

Combined EtherNet/IP Scanner/Adapter and Modbus Scanner:

NOC0321 Data Sizes.png

Michael Chan Kum Yuen
Reply

Link copied. Please paste this link to share this article on your social media post.

Richard
Lt. Commander Richard Lt. Commander
Lt. Commander

Posted: ‎2020-05-28 01:17 AM

2 Likes
2
10723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-28 01:17 AM

The main limitation for a DIO ring using RSTP is going to be that for the protocol itself. The recommendation is for no more than 40 nodes, meaning that you can have 39 devices. This will be true for both the M580 and the BMENOC0321.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2020-05-28 02:23 AM

2 Likes
5
10719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-28 02:23 AM

The previous answers are all correct. Knowing the maximum, you have to consider multiple items:

 

1: Maximum supported DIO devices:

HSBY CPU: 61 (max = 64, 3 are reserved for Ethernet/IP local slaves)

BMENOC0321: 112 (max = 124, 12 are reserved for Ethernet/IP local slaves)

 

Be aware that connecting DIO devices direct to the device ports of a HSBY CPU might not work as the CPU device ports have a VLAN active, which might not be supported by the device. To overcome this issue, use external switches or use BMENOS0200 switch in the CPU racks.

 

2: Maximum supported input/output size

HSBY CPU: 4Kbyte IN + 4Kbyte out (see previous answers)

BMENOC0321: 4Kbyte IN + 4Kbyte out (see previous answers)

Basically this means that the amount of data communicated is DIO device type dependent. You have to calculate the amount of data each device is communicating + take the overhead into consideration. I use to create some configuration and see what the data is used for each specific device type.

 

3: Maximum communication bandwith of an interface

HSBY CPU: 15000 packets

BMENOC0321: 5500 packets

The amount of packets is depending on the configured RPI (Repeat Packet Interval / Repeat Rate / update rate). For example when you define 100 devices with an RPI of 10 mS, will result in minimal 2(Read+write) * (1000/10) * 100(devices) = 20.000 packets. Solution will be to decrease the RPI for some/all devices, to keep the amount of packets between the limits.

 

4: Physical network limitation

When using a RSTP ring functionality, the limitation is to have max. 40 device within a ring. As  both CPU's count as a RSTP device, this limits the amount of DIO devices in a ring to 38. This imitation comes from fixed RSTP parameter settings in Schneider Electric DIO devices with RSTP functionality enabled (ie Modicon STB, Altivar Process). To overcome this limitation you can create a network star (using switches) or create multiple network rings (also by using switches) 

R.Roozee
Sr Solution Architect (SAE Master)
Reply

Link copied. Please paste this link to share this article on your social media post.

keithkcchan
Ensign keithkcchan Ensign
Ensign

Posted: ‎2020-06-03 10:30 PM

In response to RoozeeR
0 Likes
0
10685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 10:30 PM

Thank you all for the details explanations.

Reply

Link copied. Please paste this link to share this article on your social media post.

keithkcchan
Ensign keithkcchan Ensign
Ensign

Posted: ‎2020-06-03 10:43 PM

In response to Richard
0 Likes
0
10676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 10:43 PM

Thank you all for the details explanations.

Reply

Link copied. Please paste this link to share this article on your social media post.

keithkcchan
Ensign keithkcchan Ensign
Ensign

Posted: ‎2020-06-03 11:51 PM

In response to Richard
0 Likes
0
10668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 11:51 PM

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

keithkcchan
Ensign keithkcchan Ensign
Ensign

Posted: ‎2020-06-03 11:52 PM

In response to Michael_Chan
0 Likes
0
10667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 11:52 PM

Thank you for the information.

Reply

Link copied. Please paste this link to share this article on your social media post.

HiDwivedi
Ensign HiDwivedi Ensign
Ensign

Posted: ‎2020-07-31 12:59 AM

In response to RoozeeR
0 Likes
3
10331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-31 12:59 AM

BMENOC0321: 112 (max = 124, 12 are reserved for Ethernet/IP local slaves) 

 

Can we assume this Limitation is for one port? In this case, BMENOC0321 will be supporting 2 port X112=224 Devices leaving service port spare.

Please confirm.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Richard
Lt. Commander Richard Lt. Commander
Lt. Commander

Posted: ‎2020-08-03 04:15 AM

In response to HiDwivedi
2 Likes
2
10294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 04:15 AM

A couple of things:

 

The thread is for "Limit number of DIO devices under a DIO Main Ring". Obviously, to implement a ring you would need to use both ports.

If you were to implement two DIO clouds using the two ports, the total number of devices is dependent on the scanner not the port (see Michael's second post). This is for all ports and would still limit the total number of devices to 112.

 

If you want to connect more than 112 devices, don't forget that you can add multiple NOC modules to the configuration, each with its own scanner.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HiDwivedi
Ensign HiDwivedi Ensign
Ensign

Posted: ‎2020-08-03 05:32 AM

In response to Richard
0 Likes
1
10287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 05:32 AM

Thanks for the Information Richard,

 

I got a pretty much idea about the limitation, however here is something more I need your help to clarify, Can I use 1- Port of NOC0321 for acquiring the data from 112 Modbus TCP devices and 2nd port for connecting SCADA sending the data?

 

In this way, I want to collect data through one port and use the second port for SCADA Interface. Is it possible?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Eric_Coudurier
Lt. Commander Eric_Coudurier Lt. Commander
Lt. Commander

Posted: ‎2020-08-03 05:51 AM

In response to HiDwivedi
1 Like
0
10281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-03 05:51 AM

In a normal way the BMENOC0321 uses the 2 Control Network ports ETH2 ETH3 to communicate with the SCADA. The IO scanner is only performed on these ports(ETH2, ETH3), when the Service and the Backplane ports are configured to support IP forwarding (they are on different subnets).

In any case, it is possible to use the Control ports (ETH2 ETH3) to connect devices and SCADA but all the traffic will be on the same subnet.  Scada and devices will see all the traffic. Control Network port (ETH2 ETH3) is a dual port acting like as a switch.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of