Help transmiting data from M241 to modbus device

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Kers
Crewman
Crewman
0 Likes
1
653

Help transmiting data from M241 to modbus device

Hello guys,

 

I have created some structures in somachine in order to be transmitted with modbus from a M241 PLC. The problem is that all these data are being transmitted but not correctly. For example I have the following data:

 

W:int:=50;

VA:int:=1000;

Varpower:int:=2000;

Hz:udint:=50;

TotWhInj:ulint:=100;

TotWhAbs:ulint:=100;

 

So these data are being transmitted with modbus and I am checking with modbus poll whether the transmission is okay or not. So when I check on modbus poll I found out this:

- When I change the value of Hz (That occupy 2 modbus registers) it doesn't change the registers of Hz but change one register of Hz (The second one) and the first register of the next variable. 

 

I am not sure why that is happening. But what I know is that If change the types from udint and ulint to uint everything works fine.

 

If someone could help me I would appreciate a lot. Thanks in advance!

 

 

Tags (1)
1 Reply 1
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
0
628

Re: Help transmiting data from M241 to modbus device

You may find that the structure is effectively even word aligned because of the udint.

There could be a dummy word inserted after the Varpower variable so the Hz variable is sitting on an even word boundary.

If this was a Modicon M340 or M580, that is exactly what we would get.

There is some description on Help at this location:

Machine Expert > V1.2 > Controllers > M241 Logic Controllers > M241 Logic Controller - Programming Guide > Memory Mapping