Error light is blinking in I/O modules. I am using M580 plc and this is M580 remote drop. Everything was in working condition and even all feedback & commands were working, After few months this problem started. I gave power cycle but the problem didn't solved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-10 10:51 PM
Please check to see what has recently changed. It seems odd that you have two ethernet cables one plugged into the service port (ETH1 - No RSTP) and the second into the control port (ETH2 - RSTP). I would expect to see two cables connected to both control ports (ETH2 & ETH3).
If the cable in the service port is part of the main ERIO I would move the cable from the service port to the control port (ETH3).
If the cable is connected to devices downstream of the CPU, I would consider:
1. check your 24VDC supply.
2. Check your ethernet cables.
3. See if a new switch or something else has been placed in the main ERIO ring. Only the DRS switch should be placed in the main ERIO ring.