Hi All,
I was trying to do the data log in M251 controller using the standard instructions "Log Record". If there are multiple data in the single scan then the system does not log the records.
For Example, I am trying to capture the cold cycle as below. but it only logs first message but rese of the message is omitted. can you please advise or guide to log the record multiple records continuously in the single scan.
Quote----------------------------------------------------------------
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-06 09:59 AM
Hello,
You can CONCATENATE three messages ,
Or create a case statement for a sequential log
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-11 09:23 PM
Hi Engineer_MG,
thanks for the reply. But it was just an example.
My concern is in the same Scan of the controller there are multiple logs to be done. this is not happening.
now after several approach, I am using an work around method to log into an file system which has an array of 400 String and then using the log function to log the data.
this was helpful from "LeTomas"
EcoStruxure Machine Expert Training - Mx.x Easy logger
But was looking for an better solution if avaliable.