Hi, I have a web visualization on a TM251. My problem is when I go to the visualization I'm prompted with a login.
I don't need the user to log in, so how can I remove the authorization.
I have protection on the plc to do changes in Machine Expert, and I will like to keep that. Just not for the visualization
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-27 12:49 AM
Hello,
i check this topic and will come back to you next week with an answer.
Best regards
Max
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-01 01:23 PM
There should be more settings for the user rights management in EcoStruxure Machine Expert v2.0. It should be more modular and allow more flexibility to keep the user right protection on the program but to disable it on the Web Visualization.
EcoStruxure Machine Expert v2.0 is planned to release this spring.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-22 12:41 AM
Hello,
any news about this?
I have actually the problem on a M241 with ESME V2.0.1
Regards
Jochen
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-22 12:52 AM
rom EcoStruxure Machine Expert V2.0, it is now possible to disable User Rights for the Web Visu only on M241/251 and M262 controllers.
It means User Rights remain active for other services.
To do that, User must create the empty file WebVisuNoLogin.cfg (see attachment) into the folder /usr/Visu and reboot the controller.
After this action, no password is required to connect to the web visualization.
WebVisuNoLogin.cfg file can be downloaded to the controller through FTP Server connection or from EcoStruxure Machine Expert (MyController >> Files tab).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.