Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Communicating with Multiple M262 PLCs

Machine and Motion Control Forum

Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Machine and Motion Control Forum
  • Communicating with Multiple M262 PLCs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
FernandoRodrigues
FernandoRodrigues Support
7
LeTomas
Lt. Commander LeTomas Lt. Commander
5
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Machine and Motion Control Forum
Start a Topic
Solved
jhickman
jhickman
Cadet

Posted: ‎2025-01-07 03:07 PM

0 Likes
1
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-07 03:07 PM

Communicating with Multiple M262 PLCs

Hello all, I am a new Schneider PLCs.  We are trying to set up a M580 to communicate with a primary M262.  I think I have set this up correctly watching a training video from Leandro.  Where this comes into question is the primary M262 needs to get data from five other M262s.  When I set up the generic slave for the primary M262 I need to set a unit ID.  First question is I cannot find how to set the device ID in the M262 which is configured in the Generic Modbus config tab.  I know I can add multiple TCP slaves but is this the best course of action or should I use another protocol for the primary M262 to communicate with the five other M262s.  The reason we are setting this up is we have over 300 M262s in the building and we want to decrease the number of PLCs the M580 needs to communicate with so our primary will be just a data collector from the other five.

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FernandoRodrigues
FernandoRodrigues Support
Support

Posted: ‎2025-01-09 12:23 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 12:23 AM

Hello,
Between M262s, you can use the NVL - Network Variable List, saving a lot of effort.

https://product-help.schneider-electric.com/Machine%20Expert/V2.2/en/SoMProg/index.htm#t=SoMProg%2FD...

Needs to be properly configured to avoid broadcasting data over the whole network but for sure it's a good option for your case.

 

There is also a Leandro's video about it: https://www.youtube.com/watch?v=aaCMivqafAE

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
FernandoRodrigues
FernandoRodrigues Support
Support

Posted: ‎2025-01-09 12:23 AM

0 Likes
0
976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 12:23 AM

Hello,
Between M262s, you can use the NVL - Network Variable List, saving a lot of effort.

https://product-help.schneider-electric.com/Machine%20Expert/V2.2/en/SoMProg/index.htm#t=SoMProg%2FD...

Needs to be properly configured to avoid broadcasting data over the whole network but for sure it's a good option for your case.

 

There is also a Leandro's video about it: https://www.youtube.com/watch?v=aaCMivqafAE

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore