I am currently working on setting up ladder logic in EcoStruxure Machine Expert Basic. I have connected an ATV12 Variable Frequency Drive (VFD) to a Schneider PLC TM200C16R via Modbus RS485 communication.
I require assistance with the following:
I have already created a ladder logic program, which I am attaching here. Could you please review it and provide guidance on any necessary improvements or corrections?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 10:14 PM
Hi, in Machine Expert Basic is a sample Project (called TVDA) integrated which shows you to integrate a ATV12 ond TM2xx. The project is for TM221 but the way on TM200 should be identical.
You need to configure in the ATV12 that the command and the speed are set via modbus RTU and not via terminal.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 10:14 PM
Hi, in Machine Expert Basic is a sample Project (called TVDA) integrated which shows you to integrate a ATV12 ond TM2xx. The project is for TM221 but the way on TM200 should be identical.
You need to configure in the ATV12 that the command and the speed are set via modbus RTU and not via terminal.