A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Posted: 2020-07-08 07:39 AM . Last Modified: 2020-10-06 06:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-08 07:39 AM . Last Modified: 2020-10-06 06:38 AM
Hi,
can be set, to make the modbus server respond to function 4 (read input register ) ?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-20 06:58 AM
@AmeliaFaraci : Could you help?
Rodrigo G.
Industrial Automation Community manager
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-21 12:11 AM
Hi @Anonymous user ,
If you take a look in the page 104 of the "Modicon M251 - Logic Controller - Programming Guide" :
If I am not wrong based on the document the FC4 is not supported for Modbus TCP Server but if the client uses FC3 you can move the %IW to %MW in the controller.
I hope this helps you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-20 11:55 PM
Hi @Anonymous user ,
A workaround could be the use of the ADDM and READ_VAR function blocks, please find below the link to download the example:
https://schneider-electric.box.com/s/bfg5ow6frqlr0lhkhweokic0j25qqg2t
If you do not know how to import it in your project you can take a look in the next video:
https://schneider-electric.box.com/s/4bvegb89udef194mavkubonmoc6pb2of
Best regards,
Letomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-04 12:02 AM . Last Modified: 2022-07-04 09:20 PM
@Anonymous user wrote: MyAccountAccess Mobile AppHi,
can be set, to make the modbus server respond to function 4 (read input register ) ?
Thanks.
The Modicon M251 Logic Controller implements both client and server services so that it can initiate communications to other controllers and I/O devices, and to respond to requests from other controllers, SCADA, HMIs, and other devices. Without any configuration, the embedded Ethernet port of the controller supports Modbus server. The Modbus Client/Server is included in the firmware and does not require any programming action from the user. Due to this feature, it is accessible in RUNNING, STOPPED and EMPTY states.
Link copied. Please paste this link to share this article on your social media post.