Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

M251 Modbus server fc4

Machine and Motion Control Forum

Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Machine and Motion Control Forum
  • M251 Modbus server fc4
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
FernandoRodrigues
FernandoRodrigues Support
7
Francesco_Begnoni
Francesco_Begnoni Support
5
LeTomas
Lt. Commander LeTomas Lt. Commander
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Machine and Motion Control Forum
Anonymous user
Not applicable

Posted: ‎2020-07-08 07:39 AM . Last Modified: ‎2020-10-06 06:38 AM

0 Likes
5
3025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-08 07:39 AM . Last Modified: ‎2020-10-06 06:38 AM

M251 Modbus server fc4

Hi, 

can be set, to make the modbus server respond to function 4 (read input register ) ?

 

Thanks.

Labels
  • Labels:
  • Modicon M2xx
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Rodrigo_Garcia
Commander Rodrigo_Garcia Commander
Commander

Posted: ‎2020-07-20 06:58 AM

0 Likes
0
2985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-20 06:58 AM

@AmeliaFaraci : Could you help?

Rodrigo G. 


Industrial Automation Community manager

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2020-07-21 12:11 AM

1 Like
0
2975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-21 12:11 AM

Hi @Anonymous user ,

 

If you take a look in the page 104 of the "Modicon M251 - Logic Controller - Programming Guide" :

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=EIO0000003089.02.pdf&p_Doc_Ref=EIO0000003089

 

If I am not wrong based on the document the FC4 is not supported for Modbus TCP Server but if the client uses FC3 you can move the %IW to %MW in the controller.

 

I hope this helps you.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2021-01-20 11:55 PM

0 Likes
1
2514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-20 11:55 PM

Hi @Anonymous user ,

 

A workaround could be the use of the ADDM and READ_VAR function blocks, please find below the link to download the example:

https://schneider-electric.box.com/s/bfg5ow6frqlr0lhkhweokic0j25qqg2t

 

If you do not know how to import it in your project you can take a look in the next video:

https://schneider-electric.box.com/s/4bvegb89udef194mavkubonmoc6pb2of

 

Best regards,

 

Letomas

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-21 06:23 PM

In response to LeTomas
0 Likes
0
2483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-21 06:23 PM

Hi Le Thomas,

 

Thanks, I'll give it a go.

 

Regards,

 

Louis.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Lindamartin
Crewman Lindamartin
Crewman

Posted: ‎2022-07-04 12:02 AM . Last Modified: ‎2022-07-04 09:20 PM

0 Likes
0
1682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-04 12:02 AM . Last Modified: ‎2022-07-04 09:20 PM


@Anonymous user wrote: MyAccountAccess Mobile App

Hi, 

can be set, to make the modbus server respond to function 4 (read input register ) ?

 

Thanks.


The Modicon M251 Logic Controller implements both client and server services so that it can initiate communications to other controllers and I/O devices, and to respond to requests from other controllers, SCADA, HMIs, and other devices. Without any configuration, the embedded Ethernet port of the controller supports Modbus server. The Modbus Client/Server is included in the firmware and does not require any programming action from the user. Due to this feature, it is accessible in RUNNING, STOPPED and EMPTY states.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore