LXM32 TM221 PTO Drive Problem

Machine and Motion Control Forum

Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Machine and Motion Control Forum
  • LXM32 TM221 PTO Drive Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
FernandoRodrigues
FernandoRodrigues Support
7
LeTomas
Lt. Commander LeTomas Lt. Commander
5
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Machine and Motion Control Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-05-20 10:40 PM . Last Modified: ‎2020-09-10 12:42 AM

2 Likes
3
4466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 10:40 PM . Last Modified: ‎2020-09-10 12:42 AM

LXM32 TM221 PTO Drive Problem

I have TM221C16T and LXM32CU90M2. I want to drive my servo with PTO. I connect to servo with SoMove and run, no problem. Then I write PLC program in SoMachine Basic. I used MC_POWER_PTO,MC_MC_MOVEVEL_PTO. I entered all parameter. But servo motor turn slowly .. I don't understand why do it ?

Attachments
Labels
  • Labels:
  • Connectivity
  • Lexium
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-06-16 12:38 AM

0 Likes
0
4379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-16 12:38 AM

Hello @Anonymous user ,

 

As a default settings Lexium32 C Scaling values are ,

 

case0.JPG

 

As you can see ScalePosNum is 1 and ScalePosDenom is 16384 , that means 16364 pulse equals to 1 rev..

 

And you are using TM221C16T , in that case you are sending Pulse and Direction via fast outputs. 

 

You can find M221's  fast output kHz information.

 

case1.JPG

 

For example if you are using 100 kHz output for Pulse and direction ,

 

100000/16384 =6,103515625 rev /sec  , and  x 60 = 366,2109375 rpm 

 

You are going to take this output. 

 

To increase the velocity you can decrease ScalePosDenom. Lets see what happen when we adjust ScalePosDenom as 2000,

 

100000/2000 = 50 rev / sec     => 50 x60 sec= 3000 rpm ,

 

As you can see you fastest output can give 100000 hz output and if your revolution pulse value is 2000 pulse ,

 

You can take 3000 rpm as an output.

 

BR

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Rodrigo_Garcia
Commander Rodrigo_Garcia Commander
Commander

Posted: ‎2020-05-27 12:54 AM

1 Like
0
4442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-27 12:54 AM

Hello @AmeliaFaraci, could you help on this?

Thanks!!

Rodrigo G. 


Industrial Automation Community manager

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-06-16 12:38 AM

0 Likes
0
4380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-16 12:38 AM

Hello @Anonymous user ,

 

As a default settings Lexium32 C Scaling values are ,

 

case0.JPG

 

As you can see ScalePosNum is 1 and ScalePosDenom is 16384 , that means 16364 pulse equals to 1 rev..

 

And you are using TM221C16T , in that case you are sending Pulse and Direction via fast outputs. 

 

You can find M221's  fast output kHz information.

 

case1.JPG

 

For example if you are using 100 kHz output for Pulse and direction ,

 

100000/16384 =6,103515625 rev /sec  , and  x 60 = 366,2109375 rpm 

 

You are going to take this output. 

 

To increase the velocity you can decrease ScalePosDenom. Lets see what happen when we adjust ScalePosDenom as 2000,

 

100000/2000 = 50 rev / sec     => 50 x60 sec= 3000 rpm ,

 

As you can see you fastest output can give 100000 hz output and if your revolution pulse value is 2000 pulse ,

 

You can take 3000 rpm as an output.

 

BR

Reply

Link copied. Please paste this link to share this article on your social media post.

Oktay
Oktay
Cadet

Posted: ‎2023-12-17 02:08 AM

0 Likes
0
2052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-17 02:08 AM

Merhaba TM221 plc ile lxm32ad72n4 kodlu servyu nasıl kontrol edebilirim bilgi verir misiniz TM241 ile CanOpen yardımıyla çok yaptım ama TM221 ile yapamıyorum daha doğrusu bilgim yok yardımcı olursanız sevinirim 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore