Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Posted: 2022-02-02 10:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 10:53 AM
We are running EcoStructure 3.2. We have email alerts setup. In the event logs we get errors that email failed to send. However they emails are actually sent. This then causes the system to generate another email. So we get lots of duplicate messages.
Any have any suggestions
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:36 AM
I figured out the issue. The SMTP profile had a timeout of 20 seconds. So the Eco system was marking the message as failed if the connection took over 20sec. Even though the system said failed it would still send the email even if it took 25secs. Since the system said failed in generated another alert.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:36 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:36 AM
I figured out the issue. The SMTP profile had a timeout of 20 seconds. So the Eco system was marking the message as failed if the connection took over 20sec. Even though the system said failed it would still send the email even if it took 25secs. Since the system said failed in generated another alert.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.