Analog Input Scaling of Partial Raw Value

Machine and Motion Control Forum

Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Machine and Motion Control Forum
  • Analog Input Scaling of Partial Raw Value
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
8
FernandoRodrigues
FernandoRodrigues Support
6
Francesco_Begnoni
Francesco_Begnoni Support
5
LeTomas
Lt. Commander LeTomas Lt. Commander
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Machine and Motion Control Forum
SEER_Controls
SEER_Controls
Cadet

Posted: ‎2023-05-04 10:40 AM

0 Likes
1
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-04 10:40 AM

Analog Input Scaling of Partial Raw Value

Hi I am new to M221 and Machine Expert Basic; and need to scale an analog input signal to a portion of its raw input value. 

 

4-20ma Input

0-100 Pressure Transmitter

 

For example on a Rockwell scaling instruction I would use something like 

(Input Min Scale = 6000 & Input Max Scale = 18500) with a scaled output of (Output Min = 0 & Output Max = 100). 
 
But it seems Machine Expert will only let me scale to the full range of the transmitter 4000 - 20000. Any help would be greatly appreciated, I have been banging my head against the wall trying to figure this out. I do think I have a good handle on moving the analog into a holding register and then converting a real number once I figure out this bit. 
 
Labels
  • Labels:
  • Modicon M2xx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2023-05-05 12:00 AM

1 Like
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-05 12:00 AM

Hi @SEER_Controls 

 

Please find below the link to the online training of the Modicon M221:

https://youtube.com/playlist?list=PLFqT6GhMpgpLClSpB1iH50OUr4N4mU763

 

In your case I recommend you to take a look into the video M8.2.

 

I have also done a "library" with a function called "FB_SCALE" you can download it from the next link:

https://app.box.com/s/e3sheiyrp72a5pj7fij1h2vzk2g5a2bv

 

Best regards,

 

LeTomas

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of