Posted: 2023-02-02 05:47 AM . Last Modified: 2023-02-02 05:58 AM
Hi all.
I have this situation: there is a frequency converter ATV630D45Y6 - 600V, 45kW. There is also a 45kW electric motor. According to the production technology, the electric motor is gradually moving away from the frequency converter (the maximum distance is 500 meters).
In the manual, I learned that it is necessary to use a dV/dt filter (I marked it in the attached figure).
But what kind of dV/dt filter - to apply - is not said. Can anyone give advice? I will be grateful.
Or maybe even use a sinus filter?
Best regards,
Ruslan Konechnykh
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-02 08:38 AM
If we open this link and look at the specification of this filter, or rather the maximum cable length, we will see the maximum length there - 400 meters. So this filter is not suitable.
https://www.se.com/ww/en/product/VW3A5104/motor-choke-215-a-for-variable-speed-drive-set-of-3/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-03 04:57 AM
Yes, it's a good variant. Thanks. But it's sinus filter. Obviously in the Schneider product line there are no filters for such an inverter and a 500m line. Maybe other manufacturers have something
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of