Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Vijeo Cİtect V7.3 Modbus Communication Problem

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Industrial Automation
  • Industry Automation and Control Forum
  • Vijeo Cİtect V7.3 Modbus Communication Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Commander Bastian_Schmitz Commander
15
LeTomas
Lt. Commander LeTomas Lt. Commander
7
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
BevanWeiss
Spock BevanWeiss
4
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
ekremkurucu
Lieutenant | EcoXpert Master ekremkurucu Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-03-12 01:51 AM

1 Like
4
7777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-12 01:51 AM

Vijeo Cİtect V7.3 Modbus Communication Problem

Hii Everyone,

 

I have to read some information via modbus. I cannot read the ULONG type data. 

Its already added 40000 and I know the issue PLC addresses (base 1)

Citect can read read couple of value (INT, UINT, or LONG type of data) but  I cannot read ULONG type of data.

 

Sorry For Bad English 🙂

 

THX.

Attachments
Labels
  • Labels:
  • Smart Operations
  • Tags:
  • modbus
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RobertSanders
Lieutenant RobertSanders Lieutenant
Lieutenant

Posted: ‎2020-03-12 02:38 AM . Last Modified: ‎2020-03-12 02:39 AM

2 Likes
3
7766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-12 02:38 AM . Last Modified: ‎2020-03-12 02:39 AM

Hi

 

Below is an extract from the Modbus help (attached), try the following parameters using the Setup Editor,  ensure the change is made on the IOServer. 

 

Note: This parameter is not applicable if you are using the protocol variant MODBUS20 or MODBUS30 to communicate with a device. Under these circumstances, a value of 3 will be hardcoded for this parameter in the driver.

 

[MODBUS]LongDataType

 

In the Modbus protocol, LONG data types defaultto a simplified implementation, with a shortened range of 0 to 99,999,999 - mode 0. Mode 2 has the samerange as mode 0, but with the register order swapped. Mode 1 supports thecomplete LONG range of -2,147,483,648 to +2,147,483,647. Mode 3 has the samerange as mode 1, but with the register order swapped.

Allowable Values: 0 to 3, where:

0 = 10000 x low register + high register
1 = 65536 x low register + high register
2 = 10000 x high register + low register
3 = 65536 x high register + low register

Default Value: 3

With this parameter, you can set different values for specific I/O devices or groups of I/O devices. See Device/group-specific parameters.

 

 

If this doesn't work we will need more information Eg what controller are you using?

 

Regards

 

Rob

See Answer In Context

Attachments
MODBUS.zip
Reply
Share
Replies 4
RobertSanders
Lieutenant RobertSanders Lieutenant
Lieutenant

Posted: ‎2020-03-12 02:38 AM . Last Modified: ‎2020-03-12 02:39 AM

2 Likes
3
7767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-12 02:38 AM . Last Modified: ‎2020-03-12 02:39 AM

Hi

 

Below is an extract from the Modbus help (attached), try the following parameters using the Setup Editor,  ensure the change is made on the IOServer. 

 

Note: This parameter is not applicable if you are using the protocol variant MODBUS20 or MODBUS30 to communicate with a device. Under these circumstances, a value of 3 will be hardcoded for this parameter in the driver.

 

[MODBUS]LongDataType

 

In the Modbus protocol, LONG data types defaultto a simplified implementation, with a shortened range of 0 to 99,999,999 - mode 0. Mode 2 has the samerange as mode 0, but with the register order swapped. Mode 1 supports thecomplete LONG range of -2,147,483,648 to +2,147,483,647. Mode 3 has the samerange as mode 1, but with the register order swapped.

Allowable Values: 0 to 3, where:

0 = 10000 x low register + high register
1 = 65536 x low register + high register
2 = 10000 x high register + low register
3 = 65536 x high register + low register

Default Value: 3

With this parameter, you can set different values for specific I/O devices or groups of I/O devices. See Device/group-specific parameters.

 

 

If this doesn't work we will need more information Eg what controller are you using?

 

Regards

 

Rob

Attachments
MODBUS.zip
Reply
Share
ekremkurucu
Lieutenant | EcoXpert Master ekremkurucu Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-03-12 04:52 AM . Last Modified: ‎2020-03-12 05:02 AM

In response to RobertSanders
0 Likes
2
7758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-12 04:52 AM . Last Modified: ‎2020-03-12 05:02 AM

Hi

Thank you for your reply.

i tried your explanation and i read the device with modbus poll program.

read the device with LONG type and I calculate the value for 0,1,2,3 type of value. It has to be 3.

I have moxa gateway Its communicate via TCP/IP but Its has 2 diffrent serial port. Computer sees like a serial port. (COM21,22).

also Inittype has to be 3. I checked from your file(modbus help).

 

Here is My configuration


! #CSE:UserItem#
[MODBUS]
#Set to '3' by XXXX on 15/11/2013 13:10:58.
InitType = 3
#Set to '3' by XXXX on 16/11/2013 23:46:49.
LongDataType = 3
#Set to '64' by XXXX on 15/11/2013 13:12:15.
MaxBits = 64

 

Im trying to read micom p127 phase to neutral value. Data type showing ULONG type.

Citect reading other LONG type of value. for ULONG can not.

Reply
Share
RobertSanders
Lieutenant RobertSanders Lieutenant
Lieutenant

Posted: ‎2020-03-13 08:46 AM

In response to ekremkurucu
1 Like
1
7727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-13 08:46 AM

I do not have a MiCOM P127 and are therefore unable to test with Citect. Citect SCADA has approximately 20 different Protocol configurations for Modbus Eg, Modbus1, Modbus20 in which the major parameters are hard coded into the Driver.

 

Check that the Citect I/O Device Protocol is set to Modbus, not Eg Modbus20, this means the parameter changes in the INI file will have an effect, unfortunately it’s a matter of trying different parameter combinations.

 

It may also be worth plugging the MiCOM directly into the PC using a USB to Serial converter and using a utility like ModScan to validate the readings.

 

 

Regards

Rob

Reply
Share
ekremkurucu
Lieutenant | EcoXpert Master ekremkurucu Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-03-13 10:35 PM

In response to RobertSanders
0 Likes
0
7721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-03-13 10:35 PM

I tried to read mb poll.

Its reading value LONG type data. Also I tried to read with LONG data type in citect. It didnt work.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.