Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-14 12:01 PM
I'm using an HMIST6400 screen that communicates with an M171P PLC (with an extension).
I inserted all the registers of the PLC variables into the Operator terminal expert software.
I have created some graphic pages in which there are objects connected to my variables, but for some of these I am having problems, in fact some objects are seen with a white box and a red border.
These objects are connected to registers found in the PLC expansion (but be careful not all the expansion objects give me these problems, some are visible correctly).
The strange thing is that if, for example, I isolate one of these elements and then put it on a different page, alone, then the object appears correctly.
Could anyone tell me why?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-17 02:52 AM
Hi,
Nice visualisation.
Your problem is that you need continous adresses in ESME HVAC. If you have one address open and not assigned EOTE will generate a communiction fault. Becaus EOTE will always optimize the communication and will read so much values in one telegram as possible. If you recalc the values in ESME HVAC and reimport them in EOTE the problem should be fixed. You know the Process how you could export values from ESME HVAC and import them in EOTE?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 12:24 PM
Hi
I have the same problem but with a M580. I don`t now how to recalc de value in the PLC and reimport them in EOTE. Could anyone tell me how to doit? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 10:19 PM
Sorry Sergio I did not have expirence with Control Expert, maybe someone else will have an idea.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.