Unable to connect A9MEM2050 to TM221CE24R

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Unable to connect A9MEM2050 to TM221CE24R
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
12
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
Logic Controller - Modicon M221

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
PauloBalbino
Crewman PauloBalbino
Crewman

Posted: ‎2023-02-28 10:27 PM . Last Modified: ‎2023-02-28 10:48 PM

0 Likes
2
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-28 10:27 PM . Last Modified: ‎2023-02-28 10:48 PM

Unable to connect A9MEM2050 to TM221CE24R

HI,

 

 I am trying to connect A9MEM2050 to PLC TM221CE24R using the PLC serial port. On the PLC when I try to read a register like 1830 (power on off counter), I am getting CommError 255, OperError: 6. 

In terms of physical connections I am connecting pin 4 (D1) of the SL1 (PLC side) to port 23 of the A9MEM2050 and pin 5 (D0) of the SL1 (PLC side) to port 24 of the A9MEM2050.

 

All the other pins (common/5v) are left unconnected. I am not using any terminator resistor between PLC and A9MEM2050 (following the recommendation from the TM221 manual)

 

(1) TM221 embedded SL1 and embedded SL2 contains fixed internal high impedance bias network resistors (4.7 kΩ). Do not use external line termination resistors (standard 150 Ω) without additional external low impedance line polarization resistors (standard 450 Ω…650 Ω) to secure a proper idle voltage state of minimum 200 mV between the D1 and D0 data lines.

 

Screenshots attached with ladder example and PLC SL1 configuration

 

Any ideas?

 

Thanks,

Paulo

 

 

 

Attachments
Labels
  • Labels:
  • Smart Design & Engineering
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2023-03-02 02:18 AM

0 Likes
1
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-02 02:18 AM

Please change the wires, so far I see they are crossed. Alternativ add or sub the Modbus Register Address 1830 with 1. They are two different versions available. Sometime products start with Modbus Register Address 1 and sometimes with 0. I´m not sure which is the true for the PLC and the Energymeter.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2023-03-02 02:18 AM

0 Likes
1
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-02 02:18 AM

Please change the wires, so far I see they are crossed. Alternativ add or sub the Modbus Register Address 1830 with 1. They are two different versions available. Sometime products start with Modbus Register Address 1 and sometimes with 0. I´m not sure which is the true for the PLC and the Energymeter.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

PauloBalbino
Crewman PauloBalbino
Crewman

Posted: ‎2023-03-02 11:52 PM

In response to Bastian_Schmitz
0 Likes
0
1099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-02 11:52 PM

Physical I/O pins are correct, addressing -1 fixed the issue. Thanks

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of