Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

The 3 Types of Industrial Safety

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • The 3 Types of Industrial Safety
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2020-06-18 04:37 AM

2 Likes
1
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-18 04:37 AM

The 3 Types of Industrial Safety

Originally published on GMI blog by GM International| June 08, 2020

 

I-3-tipi-di-sicurezza-industriale.jpg

 

Industrial safety is seen universally as a necessity, above all because a safe workplace results in a comfortable, motivating climate.

The current playing field in the realm of safety is made up of both increasingly stringent laws and regulations and the need for increased production capacity and for faster production speeds. This leads workers to operate machinery faster and at greater risk. For example, with regard to machinery safety, both equipment manufacturers and equipment operators are placing great emphasis on engineering and on the application of international standards.

On the whole, the efficacy of a safety system is not based solely on technical and regulatory aspects, but also on an in-depth functional analysis of the organization, of production processes, and of the human factor. In the past, machinery safety was largely considered a cost.

Today, safety technologies may be seen as an investment in business productivity. Products such as safety switches and relays have become fairly common. With the adoption of integrated technologies and approaches to safety, PLCs and safety mechanisms, too, have enjoyed widespread use while having a limited impact on system engineering and planning.

The overall landscape of instrumentation components and programs features solutions that are able to control everything concerning the potential risks inherent in the systems and machinery in both production and transformation processes.

In sensors, for example, fire and smoke detectors allow for automated intervention in order to eliminate the causes of fire and combustion, while detectors for gases and other airborne compounds protect the workspace around the equipment. Safety PLCs are able to inhibit improper movements and prevent the transit of unauthorized personnel through hazardous areas. Generally speaking, the use of accurate, reliable devices and instrumentation is a priority in order to reduce the levels of risk.

 

 

Functional, Electrical, Intrinsic: the 3 domains of safety

Thinking of safety in generic terms can be ambiguous, especially in relation to the global analysis of the causes of accidents and related preventive measures. As such, it can be helpful to summarize the three recognized types of industrial safety and point to the main safety laws and regulations, even though it will be impossible to provide an exhaustive picture of such a vast landscape.

 

The first concept in safety is functional safety. This type of safety depends on the proper functioning of a system or machine in response to its initial electrical, electronic and programmable parameters. The main standards that govern functional safety are ISO 13849 (Safety of machinery – Safety-related parts of control systems), IEC 62061 (Safety of machinery - Functional safety of safety-related electrical, electronic and programmable electronic control systems),
IEC 61508 (Functional Safety of Electrical/Electronic/Programmable Electronic Safety-related Systems), and IEC 61511 (Functional safety – Safety instrumented systems for the process industry sector). It is important to note that the standard ISO 13849-1 requires that, in order to assess the performance of a safety-control system, the probability of dangerous failures per hour (PFH d) is to be calculated. This indicator is calculated based on the random failure rate of all components used in a system. ISO 13849 is particularly important for PLCs in that it describes the safety functions and general requirements for the design and protection of control systems. In order to design automated systems that are totally safe for production and personnel, the reference standards are the Safety Integrity Level (SIL, i.e. IEC 62061) and Good Automated Manufacturing Practice (GAMP). Also of note is the standard ANSI/ISA-99, developed in line with existing international standards and which defines the safety levels, on a scale from 0 to 4, of the various equipment used in production processes and in operations.

 

The second type of safety that is of strategic importance in industry is electrical safety. Electrical safety is achieved by designing and constructing electrical machinery so as to avoid any direct contact with electrical cables or other electrically conductive parts. Manufacturers must also seek to avoid hazards caused by indirect contact with a ground or other conductor that happens to be under tension. The main families of standards in the field of electrical safety are EN 60204 (Safety of machinery – Electrical equipment of machines), EN 60947-5 (Low-voltage switchgear and controlgear), and NFPA 79 (Electrical Standard for Industrial Machinery) for the US market. Within the scope of these standards, the prevailing Machinery Directive bases the assessment, elimination, or reduction of risk as a principle of integrating safety in the design and construction of machinery and references ISO 12100 (Safety of machinery – General principles for design — Risk assessment and risk reduction).

 

Finally, intrinsic safety, based on the ATEX directives 2014/34/EU and 1999/92/EC, is also to be taken into account. Intrinsic safety is the technical principle of preventing the risk of fire or explosion caused by electrical devices and electronic instrumentation. At the level of power and circuitry, this safety is provided by galvanic isolation and Zener barriers. In order to create protected workspaces, photoelectric barriers, i.e. electro-sensitive devices that also ensure high levels of machinery and system productivity, are used.

To choose the right electrical device to be used, we need to know which group of explosive substances the flammable compounds that may be present belong to. For all types of fire protection, the electrical devices to be installed in an area at risk of explosion must be divided into temperature classes from T1 to T6. The device manufacturer must be able to achieve the highest safety levels for each individual device by way of specific fire-protection methods. IEC 60079-11 is one of the key standards in this regard. In short, the importance and sensitive nature of the issue of safety is set within a vast, extremely specialized regulatory framework that is constantly evolving.

  • Tags:
  • Electrical safety
  • english
  • functional safety
  • galvanic isolation
  • intrinsic safety
  • machinery directive
  • SIL
  • Zener barriers
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Rodrigo_Garcia
Commander Rodrigo_Garcia Commander
Commander

Posted: ‎2020-09-24 03:08 AM

0 Likes
0
2060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-24 03:08 AM

Thanks!

Rodrigo G. 


Industrial Automation Community manager

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore