Hi
So I'm trying to connect a coin acceptor to a M221C24T.
As I undestand it the coin acceptor (RM5 Evolution) sends a 100ms pulse everytime it recognizes a coin, however the plc is not recognizing that pulse. I've tried to configure a pulse input but have not been sucessfull.
Pretty sure ( or maybe not) that the acceptor is functioning correctly.
Need it to recognize a coin, send the pulse to the plc. What am I doing wrong?
Thank you
- Labels:
-
Workforce Empowerment
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-12 07:35 AM
Hi,
I think the problem is that the coin acceptor works with a NPN output and the TM221 has a PNP input.
In my opinion it will make sense if you test at first the output signal of the coin validator with a voltage measuring device.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-12 07:35 AM
Hi,
I think the problem is that the coin acceptor works with a NPN output and the TM221 has a PNP input.
In my opinion it will make sense if you test at first the output signal of the coin validator with a voltage measuring device.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-12 07:54 AM
Hello
I completely missed that. Your probably right,
Probably need a osciloscope that I don't have to test it, since a multimeter won't detect that pulse.
Thank you for pointing that out, completely missed it.
TY
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-25 01:48 AM
Just inverted the polarity with a relay, easy solution
Thank you for pointing thar out.
- Tags: