TC90x are powered by a 230 to 24 VAC transformer, one per bus (two in total). No earth grounded, no secondary neutral to earth, done and designed by contractors (not related to us).
If any of the buses is connected alone, the devices communicate. If both buses are connected, the nightmare appears and the connection is totally caotic.
Can anyone help us or guide us in order to detect where is the error?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-1110:46 PM
Did you connect 3wires for Modbus or 2wires? If the Gnd of the delta plc is internally connected I would suggest to remove the hand connection on line 1 and 2.