Request for Support – Communication Issue Between M580 PLC and PAS600L via DTM
  • Industrial Automation
  • Request for Support – Communication Issue Between M580 PLC and PAS600L via DTM
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Sesa460428
Crewman Sesa460428 Crewman
Crewman
Posted: ‎2025-09-17 04:53 PM
1210
We are currently working on a system upgrade project where we have migrated from a Quantum PLC (communicating with ETG100 via IO Scanning) to an M580 PLC communicating with PAS600L.
In the previous setup, IO Scanning functioned reliably and consistently. However, after the migration, IO Scanning was replaced with DTM communication. We have configured the M580 PLC to communicate with PAS600L using the DTM, but we are encountering a critical issue:
  • The DTM Browser successfully reads data only during the first poll.
  • Subsequent polls fail to retrieve any data from the PAS600L device.
We would appreciate your guidance on the following points:
  1. Are there any known limitations with the DTM Browser in continuously polling Modbus devices like PAS600L?
  2. Could you recommend a reliable method to achieve continuous data acquisition from PAS600L to M580?
  3. Are there specific configurations required in PAS600L to ensure stable communication with M580?
We would be grateful for any documentation, configuration examples, or troubleshooting steps you can provide to help resolve this issue.
Thank you for your support.
Best regards,
Krishnakumar Ramasubbu
  • Process Automation Talks
Rico94
Ensign Rico94 Ensign
Ensign
Posted: ‎2025-09-29 10:15 AM
1
978
hello, verify that the time out of the serial bus on the PAS600 (configuration PAS600 with web page) is lower than the time out of the DTM request, and select Gateway\bridge device on the DTM
Replies 7
Romain_Polette
Kirk Romain_Polette Kirk
Kirk
Posted: ‎2025-09-18 12:35 AM
Hello @Sesa460428 ,
ETG100 was an old gateway => No more support (including Modbus stack). If you still use this gateway, you may encounter some communication issue if the Modbus stack is overloaded.
Regards Panel Server, I'm not aware of any issue regarding Modbus polling.
Now, we need to understand your architecture and how PAS600 is used as a gateway:
  • What are the devices connected to the Panel Server ?
  • Serial devices only ? Some Ethernet devices ?
  • Did you set up anything on the PAS600 interface ?
  • Are you using the PAS600 as a transparent gateway ?
I do not think the M580 can "stress" the Panel Server to block the Modbus stack. I will let the PLC experts answer regarding the DTM.
Romain POLETTE
Solution Architect - France Operations
Sesa460428
Crewman
Posted: ‎2025-09-18 01:19 AM
Hi Romain,
Thank you for your prompt response!
Please find attached the existing MV System Architecture. We are currently in the process of replacing the Quantum PLC and ETG-100 with the M580 PLC and PAS600L.
In the field, we have SEPAM Series 80 devices connected via ACE949-2. For your reference, I’ve also attached screenshots from the DTM query.
Each SEPAM is configured to read from addresses 464001 and 403217, and we are writing to 3208.
Please let me know if you need any further details or clarification.
Best regards,
Rico94
Ensign
Posted: ‎2025-09-18 08:48 AM
1
1177
hello,
you are using a PAS600 as a gateway, so try to tick "gateway" for all requests.BR
Sesa460428
Crewman
Posted: ‎2025-09-28 12:21 AM . Last Modified: ‎2025-09-28 12:24 AM
In response to Rico94
Hi@Rico94 @Romain_Polette,
Thank you for your prompt response.
We are still facing issues in our setup where PAS600L is communicating with four SEPAM devices. Specifically, we’ve observed the following:
When one or more SEPAM devices lose communication, the values from other devices intermittently drop.
The freshness indicator for those values also becomes zero, even for devices that are still online.
While PLC switchover communication lost and all Input values getting zero and then it is taking time to re-establish the communication.
This behavior is affecting data reliability. Has anyone encountered similar issues or found a workaround to maintain stable data flow and freshness when partial communication loss occurs?, If you could share working backup it will be very useful for us.
Any insights or suggestions would be greatly appreciated.
Romain_Polette
Kirk
Posted: ‎2025-09-29 12:20 AM
Hello @Sesa460428 ,
I can only help for Panel Server.
I suggest to contact our tech support to faster the resolution.
Did you check if communication is OK on PAS600 side ? In case of communication loss of 1 sepam, can you still reach the other ones directly from the Panel Server web page (Read Register feature). Or with a basic Modbus Client upstream the PAS600 ?
Romain POLETTE
Rico94
Ensign
1
979
Sesa460428
Crewman
Posted: ‎2025-10-03 07:21 AM
"Thank you. Communication is now established between SEPAM and PLC, although there are some device failures. However, during PLC switchover, the values are resetting to zero. We are transferring data from the DTM to the memory location only when the freshness flag is set to one." Would you like me to help you troubleshoot the zero values during switchover? For example: Should the memory retain the last known value during switchover? Is the freshness flag being reset or delayed during the transition?