Request for Support – Communication Issue Between M580 PLC and PAS600L via DTM

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Request for Support – Communication Issue Between M580 PLC and PAS600L via DTM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
Sesa460428
Crewman Sesa460428 Crewman
Crewman

Posted: ‎2025-09-17 04:53 PM

0 Likes
7
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-17 04:53 PM

Request for Support – Communication Issue Between M580 PLC and PAS600L via DTM

We are currently working on a system upgrade project where we have migrated from a Quantum PLC (communicating with ETG100 via IO Scanning) to an M580 PLC communicating with PAS600L.

In the previous setup, IO Scanning functioned reliably and consistently. However, after the migration, IO Scanning was replaced with DTM communication. We have configured the M580 PLC to communicate with PAS600L using the DTM, but we are encountering a critical issue:

  • The DTM Browser successfully reads data only during the first poll.
  • Subsequent polls fail to retrieve any data from the PAS600L device.

We would appreciate your guidance on the following points:

  1. Are there any known limitations with the DTM Browser in continuously polling Modbus devices like PAS600L?
  2. Could you recommend a reliable method to achieve continuous data acquisition from PAS600L to M580?
  3. Are there specific configurations required in PAS600L to ensure stable communication with M580?

We would be grateful for any documentation, configuration examples, or troubleshooting steps you can provide to help resolve this issue.

Thank you for your support.

Best regards,
Krishnakumar Ramasubbu

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rico94
Ensign Rico94 Ensign
Ensign

Posted: ‎2025-09-29 10:15 AM

0 Likes
1
188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-29 10:15 AM

hello, verify that the time out of the serial bus on the PAS600 (configuration PAS600 with web page) is lower than the time out of the DTM request, and select Gateway\bridge device on the DTM

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-09-18 12:35 AM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 12:35 AM

Hello @Sesa460428 , 

ETG100 was an old gateway => No more support (including Modbus stack). If you still use this gateway, you may encounter some communication issue if the Modbus stack is overloaded.

 

Regards Panel Server, I'm not aware of any issue regarding Modbus polling.


Now, we need to understand your architecture and how PAS600 is used as a gateway:

  • What are the devices connected to the Panel Server ?
  • Serial devices only ? Some Ethernet devices ?
  • Did you set up anything on the PAS600 interface ?
  • Are you using the PAS600 as a transparent gateway ?

I do not think the M580 can "stress" the Panel Server to block the Modbus stack. I will let the PLC experts answer regarding the DTM.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply

Link copied. Please paste this link to share this article on your social media post.

Sesa460428
Crewman Sesa460428 Crewman
Crewman

Posted: ‎2025-09-18 01:19 AM

0 Likes
0
397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 01:19 AM

Hi Romain,

Thank you for your prompt response!

Please find attached the existing MV System Architecture. We are currently in the process of replacing the Quantum PLC and ETG-100 with the M580 PLC and PAS600L.

In the field, we have SEPAM Series 80 devices connected via ACE949-2. For your reference, I’ve also attached screenshots from the DTM query.

Each SEPAM is configured to read from addresses 464001 and 403217, and we are writing to 3208.

Please let me know if you need any further details or clarification.

Best regards,
Krishnakumar Ramasubbu

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Rico94
Ensign Rico94 Ensign
Ensign

Posted: ‎2025-09-18 08:48 AM

1 Like
1
387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 08:48 AM

hello,

you are using a PAS600 as a gateway, so try to tick "gateway" for all requests.BR

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Sesa460428
Crewman Sesa460428 Crewman
Crewman

Posted: ‎2025-09-28 12:21 AM . Last Modified: ‎2025-09-28 12:24 AM

In response to Rico94
0 Likes
0
258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-28 12:21 AM . Last Modified: ‎2025-09-28 12:24 AM

Hi@Rico94 @Romain_Polette,

 

Thank you for your prompt response.

We are still facing issues in our setup where PAS600L is communicating with four SEPAM devices. Specifically, we’ve observed the following:

When one or more SEPAM devices lose communication, the values from other devices intermittently drop.

The freshness indicator for those values also becomes zero, even for devices that are still online.

While PLC switchover communication lost and all Input values getting zero and then it is taking time to re-establish the communication.

This behavior is affecting data reliability. Has anyone encountered similar issues or found a workaround to maintain stable data flow and freshness when partial communication loss occurs?, If you could share working backup it will be very useful for us.

Any insights or suggestions would be greatly appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-09-29 12:20 AM

0 Likes
0
206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-29 12:20 AM

Hello @Sesa460428 , 

I can only help for Panel Server.

I suggest to contact our tech support to faster the resolution. 

 

Did you check if communication is OK on PAS600 side ? In case of communication loss of 1 sepam, can you still reach the other ones directly from the Panel Server web page (Read Register feature). Or with a basic Modbus Client upstream the PAS600 ?

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply

Link copied. Please paste this link to share this article on your social media post.

Rico94
Ensign Rico94 Ensign
Ensign

Posted: ‎2025-09-29 10:15 AM

0 Likes
1
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-29 10:15 AM

hello, verify that the time out of the serial bus on the PAS600 (configuration PAS600 with web page) is lower than the time out of the DTM request, and select Gateway\bridge device on the DTM

Reply

Link copied. Please paste this link to share this article on your social media post.

Sesa460428
Crewman Sesa460428 Crewman
Crewman

Posted: ‎2025-10-03 07:21 AM

In response to Rico94
0 Likes
0
103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-03 07:21 AM

"Thank you. Communication is now established between SEPAM and PLC, although there are some device failures. However, during PLC switchover, the values are resetting to zero. We are transferring data from the DTM to the memory location only when the freshness flag is set to one." Would you like me to help you troubleshoot the zero values during switchover? For example: Should the memory retain the last known value during switchover? Is the freshness flag being reset or delayed during the transition?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore