OFS Server Preloading on building changes in a program intrupts Citect Communication..
  • Industrial Automation
  • OFS Server Preloading on building changes in a program intrupts Citect Communication..
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
hemant2309
Crewman hemant2309
Crewman
Posted: ‎2024-03-22 06:06 AM
Hi All,
I have M580 redundant controller communication configured with Citect SCADA using OFS Server 3.62.
Whenevar i build changes specifically on adding a new variable, OPC Server goes in preloading state which Stops SCADA communication for a time when OFS server is in preloading stage.
I found similar discussions on a community and they suggested following settings to verify..
1. use the latest OFS current version is 3.63.4902
2. In the PLC embedded data settings make sure the following are checked:
Use data dictionary
No communication break
3. if needed you can adjust the effective build changes time-out starting at 40 if
4. preload on build changes may also improve the process.
out of 4, Sr no. 2,3,4 are already done however its does not help..
Does Changing to OFS version to V3.63 or above is the only solution for this issue or are there are settings as well?
Your reply will be apreciated..
regards
Hemant
  • Process Automation Talks
Replies 0