Modbus server is not responsive.
  • Industrial Automation
  • Modbus server is not responsive.
Bastian_Schmitz
34
LeTomas
14
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
6
msthrax
msthrax
Cadet
Posted: ‎2024-07-23 02:10 AM
310
Hello
I'm using Schneider TM200CE24R PLC in my project. I have to link two PLCs with two radio devices(Mikrotik) in a long distance. These two PLCs are working normal but an special situation occurs after some hours usually. PLC1 reads some registers from PLC2 in a constant interval(around 10s). The radio connection is poor and timeouts happens sometimes. I think sometimes when PLC1 tries to connect and read data from PLC2 some packet loss and timeouts happens and the socket stays open and occupy one network socket. Next time this happens again and again. The PLC datasheet says it has 8 network sockets total.
I think these 8 sockets got occupied and I can't connect to PLC2 anymore neither"Machine Expert" software or Modbus TCP. When I turn off and on the PLC it works ok or I reprogram it.
My question is how can I find the number of sockets occupied and how can I reset the PLC or release network resources occupied by any object or request?
  • Smart Design & Engineering
Bastian_Schmitz
Admiral
Posted: ‎2024-07-24 12:10 AM
How do you communicate? Via IO Scanner or manually?
You could check this system Word