Hello,
i have small project i have to connect "HMIGXU3512" hmi to S7-300 PLC (existing plc),
I have an issue about the cable i should use, really i found a document file in the website about "MPI/PPI Driver" from the document i reach to the following pin out
please not that this connection not working for me, please support me to understand where the issue could happen. or is there is a better solution?
Best Regards,
|
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-03 01:37 AM
MPI/PPI is bus based on RS485. In that case the wiring is nearly like you described. On the Connector of SE/PF HMIs you need to make a shortcut between 3(SDA)+1(RDA) and 7(SDB)+2(RDB).
This need result of the possibility that you could use the connector for RS485/RS422.
You could find this information on the follow documentation on page 37
The additional connections are only needed on other HMIs were the COM support RS4** and RS232.