Posted: 2025-02-09 11:55 PM
M580 Max Input Real/Float Value
Does anyone know what is the Floating/Real Value range for M580 Modi con Input.
As far as i know 3.402E+38 is max
1. I am trying to use a totalizer block and when i pass Max real to Input it goes to Infinity 1#INF
2. Could you suggest some Min Positive real value for Modi con M580 Input
- Labels:
-
Process Automation Talks
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-11 11:48 AM
Yes, IEEE max float is 3.4028235e38.
But what are you trying to do? Why would you pass 3.402E+38 to the input of totaliser? Or am I mis-understanding? If the totaliser itself is accumulating up to 3.402E+38, then you should consider using more appropriate engineering units on the input. And don't forget to set a suitable Threshold parameter (I usually just use 10000).
If you do need to have very large numbers, you would be better doing a smaller accumulation and then incrementing a UDINT (using appropriate engineering units).