M221 serial line stuck (stress test)

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • M221 serial line stuck (stress test)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
PauloBalbino
Crewman PauloBalbino
Crewman

Posted: ‎2024-03-04 11:02 PM . Last Modified: ‎2024-03-04 11:05 PM

0 Likes
0
861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-04 11:02 PM . Last Modified: ‎2024-03-04 11:05 PM

M221 serial line stuck (stress test)

As part of the pre-commissioning testing, we validate ladder logic against different scenarios, one of them is related to testing the serial line adding noise, parity errors, drop of frames, insert/remove out extra characters to the frame, ignore requests, delay responses.

 

PLC/Ladder is properly able to handle the scenario when requests are ignored (sensor disconnected) and when the response is delayed. But when we test introducing parity errors (CRC) or any other simulation that actually corrupts the frame, after some time (5 min to 10 min) the READ_VAR blocks get stuck and the only way to properly get the communication back is to restart the PLC. 

 

(Check attachments)

Image 1: Test using PLC connected to a Rs485 to USB adapter and using a simulator (ModRSim2 OpenSource)

 

Serial devices:

(Check attachments)

Image 2: List of READ_VARs

 

Comm port settings:

Image 3: (Check attachments)

 

 

How to replicate the issue:

1 - Setup the environment similarly to image 1.

2 - Configure the READ_VARs as in image 2.

3 - Add the READ_VARs on the ladder, sequentially after one finishes trigger the next. DONE or ERROR triggers EXECUTE of the next. (in our case we have a counter adding a small delay between each READ_VAR)

3 - Download and install ModRsSim2 https://sourceforge.net/projects/modrssim2/

4 - Under "Communication Fault Simulation" enable all options.

5 - Let it run for 10 min

6 - Monitor the errors on each READ_VAR

 

After getting "stuck" every new read attempt on any READ_VAR (EXECUTE to 1) fails (ERROR to 1) with the following error codes:

 

 CommError: 255

 OperError:  6

 

 

Is there any limitation or known issue on the serial port SL (READ_VAR communication block)?

Attachments
Labels
  • Labels:
  • Energy Efficiency
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore