Hello
I turn to you because I am going in circles.
I would like to retrieve counter information by ioscanner mode on port SL1.
but no frames start from m221. the led remains off.
i have tested with basic expert machine example program, but it does not work.
An idea ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-05-12 07:38 AM
Excellent @Anonymous user that is working!
In order to check if you have a problem with a device on IOScanner you need to check the System objects IOScanner status.
Depend on the IOscanner selected it start with:
In your case your device over modbus serial will be %IWNS10x.
The value of that variable will give you the status:
In the next example I am using the ethernet that's why it start with %IWNS30x but it is the same, you just need to check the status:
In this example the first device on the IOscanner is disconnected from the network so the status is 6. The second device is connected to the M241 and it is working fine, the status is 2.
If this solves the problem remember to mark this coments as part of the solution for this π.
Best regards,
LeTomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-05-12 12:19 AM
Hi @Anonymous user
For my comment I am going to assume that:
You should check the status of the IOScanner Serial Line (1) . I recommend you to create an Animation table:
Check the %SW210:
If the %SW210 is not equal to "2" you can set to 1 the %S110 to reset the IOScanner.
Best regards,
LeTomas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-05-12 07:03 AM
hi @LeTomas
I tested and it was successful.
your indications guided my diagnosis.
the next problem is the management of communication faults.
my bench is composed of a single device. but in a month, I would have all the counters. then for anticipated.
1 / how do I manage faults, device by device ?
2 / what is the device's communication fault bit ?
Thank
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-05-12 07:38 AM
Excellent @Anonymous user that is working!
In order to check if you have a problem with a device on IOScanner you need to check the System objects IOScanner status.
Depend on the IOscanner selected it start with:
In your case your device over modbus serial will be %IWNS10x.
The value of that variable will give you the status:
In the next example I am using the ethernet that's why it start with %IWNS30x but it is the same, you just need to check the status:
In this example the first device on the IOscanner is disconnected from the network so the status is 6. The second device is connected to the M241 and it is working fine, the status is 2.
If this solves the problem remember to mark this coments as part of the solution for this π.
Best regards,
LeTomas