Hello team,
I want to use a M221 to permanently check some Modbus registers on few Panel Servers. In case of any change on a specific register, I want to trigger an output of the M221. Final goal is to use M221 as an alarm relay because HeatTag device doesn't have a dry contact to connect to a relay / PLC.
My architecture looks like below.
In this case:
I know I can use the Modbus TCP IO Scanner feature of the M221, but I do not know the limits...
How many Panel Server can the IO Scanner read permanently ? Any limitation regarding the total number of registers ?
Thanks for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-04 11:51 PM . Last Modified: 2025-07-05 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-06 11:47 PM
Hi @Romain_Polette ,
You can have up to 16 devices configured on the IOScanner of the M221 when you use it over ModbusTcp.
Then per device (If I am not wrong) you can add up to 10 channels.
If you need more then I recommend you to go to another device like the M251 or M172.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-04 11:51 PM . Last Modified: 2025-07-05 12:22 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-06 11:47 PM
Hi @Romain_Polette ,
You can have up to 16 devices configured on the IOScanner of the M221 when you use it over ModbusTcp.
Then per device (If I am not wrong) you can add up to 10 channels.
If you need more then I recommend you to go to another device like the M251 or M172.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-06 11:58 PM
Thanks for your help @ismailozinan and @LeTomas .
Regards,