How to read more than 125 Registers in Modbus TCP/IP through DTM Broeser?

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • How to read more than 125 Registers in Modbus TCP/IP through DTM Broeser?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
AhmadJamal1997
Crewman AhmadJamal1997
Crewman

Posted: ‎2025-05-23 08:13 AM

0 Likes
3
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-23 08:13 AM

How to read more than 125 Registers in Modbus TCP/IP through DTM Broeser?

 

Hello,

I'm trying to read around 190 registers by DTM Browser in M580 through BMENOC301_2:

1. First Request: 125 Registers.

2. Second Request: 71 Registers.

 

125+71 Registers.png

 

but I received only the first 125 Regiters, Can I toggle the requests cyclically by disabling connection bits (I don't know where they are)?

 

 

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • BMENOC301_2
  • DTM browser
  • english
  • m580
  • Modbus TCP IP
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
ciupol
Lieutenant ciupol
Lieutenant

Posted: ‎2025-05-28 05:25 AM

0 Likes
1
129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-28 05:25 AM

You shouldn't need to toggle connection bits. All the registers should be read. A device DDT is created for this connection. See below. Free0 is the data for your first request and Free1 is the data for your second request.

ciupol_0-1748435126108.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AhmadJamal1997
Crewman AhmadJamal1997
Crewman

Posted: ‎2025-05-31 05:02 AM

In response to ciupol
0 Likes
0
76
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-31 05:02 AM

Thanks for your reply @ciupol 
I have already implemented it the same way, but it didn't work.

It only accepts the first request.

DTM Browser.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
Lieutenant ciupol
Lieutenant

Posted: ‎2025-06-02 06:52 AM

0 Likes
0
46
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-02 06:52 AM

Not sure what you are communicating with but is it possible that your Modbus device supports only single connection?

 

According to NOC301 manual (below), turning connections ON/OFF is possible by object ID. I have never done this and I am not sure what does that mean.

ciupol_0-1748872227273.png

 

If your device truly supports only single connection it may be easier for you to use READ_VAR block rather then use DTM browser.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of