Hello,
I'm trying to read around 190 registers by DTM Browser in M580 through BMENOC301_2:
1. First Request: 125 Registers.
2. Second Request: 71 Registers.
but I received only the first 125 Regiters, Can I toggle the requests cyclically by disabling connection bits (I don't know where they are)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-28 05:25 AM
You shouldn't need to toggle connection bits. All the registers should be read. A device DDT is created for this connection. See below. Free0 is the data for your first request and Free1 is the data for your second request.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-31 05:02 AM
Thanks for your reply @ciupol
I have already implemented it the same way, but it didn't work.
It only accepts the first request.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-02 06:52 AM
Not sure what you are communicating with but is it possible that your Modbus device supports only single connection?
According to NOC301 manual (below), turning connections ON/OFF is possible by object ID. I have never done this and I am not sure what does that mean.
If your device truly supports only single connection it may be easier for you to use READ_VAR block rather then use DTM browser.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of